This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus Question
#6
(04.07.2024, 07:29)admin Wrote: Can you read this register value using read test? When using bitmask for a single bit in a register you can set bus_datatype to "bool".

Yes, I can read this register value. I also can change the mode of the heat pump through the Iglu app and get feedback into the LM address "41/1/3." However, if I try to set the same numbers I see when I activate active cooling through the app, it doesn't work. In the LM, I see that the value in the address "41/1/3" is 128 when active cooling is activated and 16 when active cooling is off. When I try to set values in the address "41/1/3" I still cannot control the mode directly.


Ok I will change bus type to bool Smile
Reply


Messages In This Thread
Modbus Question - by gtsamis - 29.06.2024, 10:50
RE: Modbus Question - by Erwin van der Zwart - 29.06.2024, 10:58
RE: Modbus Question - by gtsamis - 29.06.2024, 11:30
RE: Modbus Question - by Osvaldas - 04.07.2024, 07:24
RE: Modbus Question - by admin - 04.07.2024, 07:29
RE: Modbus Question - by Osvaldas - 04.07.2024, 08:05
RE: Modbus Question - by admin - 04.07.2024, 08:41
RE: Modbus Question - by Osvaldas - 04.07.2024, 10:07
RE: Modbus Question - by Daniel - 04.07.2024, 10:09
RE: Modbus Question - by Osvaldas - 04.07.2024, 10:26
RE: Modbus Question - by Daniel - 04.07.2024, 10:29
RE: Modbus Question - by Osvaldas - 04.07.2024, 11:42

Forum Jump: