6 hours ago
Use Read test to find correct settings. You might need to use a different swap mode. Why do you map int32 to float32? This is not needed if you are using the value directly without setting value_multiplier.
Modbus Profile incorrect value
|
« Next Oldest | Next Newest »
|
Messages In This Thread |
Modbus Profile incorrect value - by AlexLV - Yesterday, 22:00
RE: Modbus Profile incorrect value - by admin - 6 hours ago
RE: Modbus Profile incorrect value - by AlexLV - 59 minutes ago
RE: Modbus Profile incorrect value - by admin - 53 minutes ago
|