This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

conection
#2
Hi,

1) Make sure the filter tables are correct in the IP routers and during testing try with all filters open, after that you can add restricted filter settings.
2) Make sure all KNX routers and SL are in the same network scope like 192.168.0.xxx and that all KNX multicast addresses are the same and correct (default = 224.0.23.12).
3) Make sure KNX IP Features is enabled in the SL's KNX settings.
4) Make sure all routers have correct zone / line address like 1.0.0, 1.1.0, 1.2.0, 1.3.0.

If you follow steps above it should work..

BR,

Erwin
Reply


Messages In This Thread
conection - by balatis - 03.05.2018, 11:49
RE: conection - by Erwin van der Zwart - 03.05.2018, 17:36
RE: conection - by balatis - 04.05.2018, 10:47
RE: conection - by Erwin van der Zwart - 04.05.2018, 12:06
RE: conection - by balatis - 06.05.2018, 19:21
RE: conection - by Erwin van der Zwart - 06.05.2018, 20:31
RE: conection - by balatis - 21.05.2018, 09:47
RE: conection - by Daniel - 21.05.2018, 10:14
RE: conection - by balatis - 21.05.2018, 10:34
RE: conection - by admin - 21.05.2018, 10:57
RE: conection - by Daniel - 21.05.2018, 10:58
RE: conection - by balatis - 21.05.2018, 11:26
RE: conection - by Daniel - 21.05.2018, 11:40
RE: conection - by balatis - 21.05.2018, 11:46

Forum Jump: