This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus SunSpec support
#3
The correct address is probably not 40188, but either 187 or 188. You can check this quickly with RTU test. If you want to create a profile, then address_scale field should be used to tell where to read the scaling factor from.
Reply


Messages In This Thread
Modbus SunSpec support - by joost001 - 22.05.2017, 20:11
RE: Modbus SunSpec support - by mlaudren - 22.05.2017, 21:43
RE: Modbus SunSpec support - by admin - 23.05.2017, 06:58