Read with Wait function
Hello
I'm looking for a function which sends read request to KNX bus and waits for the result. The reason is I have two inputs which I need to be sure their values are actual.
This works but it's ugly because I don't check if the readings of both values were successful:
grp.read('6/4/28')
grp.read('6/4/45')
os.sleep(5)
val_a=grp.getvalue('6/4/28')
val_b=grp.getvalue('6/4/45')
Is there such
err,val_a=grp.readAndWait('6/4/28')
Use this function:
12345678910111213141516171819202122232425262728293031323334
function readresponse(alias, timeout)   local obj, lb, ts, tu, delta, value   obj = grp.find(alias)   if not obj then     return nil, 'object not found'   end   timeout = timeout or 3   lb = require('localbus').new(timeout / 10)   lb:sethandler('groupresponse', function(event)     if event.dst == obj.address then       value = busdatatype.decode(event.datahex, obj.datatype)     end   end)   grp.read(obj.address)   ts, tu = os.microtime()   repeat     lb:step()     delta = os.udifftime(ts, tu)   until value ~= nil or delta >= timeout   if value ~= nil then     return value   else     return nil, 'timeout'   end end res, err = readresponse('0/0/3') log(res, err)
Excellent as usual Admin. Thank you.
But does lb:step() do yield? Isn't the cycle utilising the CPU to 100%?
It returns once a single local bus message has been received or timeout happens. Script does not consume CPU while waiting.
Is it possible for the timeout to re-trigger and over ride the last timeout every time the function i called? i am having a few instances running at the same time
Do you mean that you want to send several read requests at once and then return once all responses are received or timeout happens?