Hi everybody!  Big Grin
I have a big problem, with the execution of my project and I hope you will have some advise.
I have to read/write datas from/to 4 different PLCs in the same Modbus RTU network. There are 14 different script (6 resident, 6 event and 2 scheduler) that exchange data via modbus RTU.
To avoid that one or more script start before the finish of the script that is in execution, I use this code:
repeat  tmp = storage.get("Modbus")  if (tmp == nil or tmp == 0) then    storage.set("Modbus", 1)    continue = true    alert("--SCRIPT--Dati CT -> START")    --This line is used for debuggig purpose  else    continue = false    os.sleep(0.2)  end until (continue) --My script code that start communication with one modbus slave PLC
Sometimes it happened that 2 or more script started at the same time and they were both executed. This couse timeout and wrong slave errors because scripts set the communication with different slaves.
I hope you will understand my problem, I'm not very good in english Tongue
Mirco
You can use built-in modbus mapper and create a profile for each PLC. This way you won't have any sync issues. You can also use modbus mapper as a proxy, I'll provide an example later on.
(13.09.2016, 07:17)admin Wrote: You can use built-in modbus mapper and create a profile for each PLC. This way you won't have any sync issues. You can also use modbus mapper as a proxy, I'll provide an example later on.
I can't, because I have to manipulate datas before writenig it into an object (for example: my PLC use 2 byte integer registers, and I have to convert it in 2 byte float for the visualization) or I have to don't read some registers if a condition is checked.
You can use proxy which will be available in RC2 firmware. First, you have to enable RTU in modbus mapper, then you can use it in scripts like this:
mbproxy = require('mbproxy') mb = mbproxy.new() mb:setslave(2) r1, r2, r3 = mb:readregisters(0, 3) log(r1, r2, r3)
In your code you will just have to replace luamodbus require/open/connect with proxy functions and you won't have any issues with simultaneous port access from several scripts Smile
(14.09.2016, 08:40)admin Wrote: You can use proxy which will be available in RC2 firmware. First, you have to enable RTU in modbus mapper, then you can use it in scripts like this:
Thanks for your help!  Smile I tried it yesterday, but unfortunatelly the Schneider HomeLYnk and SpaceLYnk.. (Next time I will buy your LogicMachine)
Do you have a library that can I import, or something else that can I do?
Thanks again for your help!
Please contact us via e-mail
Does this code work if I use Modbus TCP instead of Modbus RTU?
No, there's no point as TCP can be used simultaneously unlike RS485.
Is this solution validated yet in Wiser / SL 2.1.1 ?