20.06.2021, 11:22 (This post was last modified: 20.06.2021, 12:07 by Bobby.)
Hi!
I have 2 pcs of https://openrb.com/dali-rs485-gateway/ .
The have worked ok for a long time, but suddenly GW-1 stopped working.
It shows up in the interface, but none of the lamps connected to it responds.
Tried restarting the whole system, tried updating to the last FW on my reactor v3, but still dead.
All of the lights connected to the GW-2 works fine. Any suggestions how to trace the fault?
Both of the GW has the same 24V Power supply, as well as 18V PS for the DALI.
Both of them measures 15V Out to the DALI line....
"reply timeout" means that the gateway sent the request to the DALI bus but there was not reply. This indicates that at least the RS-485 communication part on the GW-2 is working correctly. Check the RS-485 wiring for GW-1 and also check if the on-board LED turns on when the on-board button is pressed.
(21.06.2021, 06:39)admin Wrote: "reply timeout" means that the gateway sent the request to the DALI bus but there was not reply. This indicates that at least the RS-485 communication part on the GW-2 is working correctly. Check the RS-485 wiring for GW-1 and also check if the on-board LED turns on when the on-board button is pressed.
Hi!
Checked the wiring yesterday, From lm -> GW1 -> GW2 ok.
Tested the led, ok. works on both.
You can but you need an external power supply for this. If the gateway power part is still working you can connect the DALI from the gateway to your Reactor.
21.06.2021, 12:18 (This post was last modified: 21.06.2021, 12:19 by Bobby.)
(21.06.2021, 12:14)admin Wrote: Send us an e-mail please. The answer might take some time as office is closed this week due to public holidays.
Message sent
(21.06.2021, 12:18)admin Wrote: You can but you need an external power supply for this. If the gateway power part is still working you can connect the DALI from the gateway to your Reactor.
Ok, i will try that.
Is there a way to backup the mapping of the lamps, or do i have to do all of the lamps again?