Framing error on DALI RS485 gateway
I'm using the DALI RS485 gateway for LogicMachine (LM5Lp2), but I am having trouble scanning for devices in the DALI tab on the web interface of LogicMachine.
When I try to scan for devices, I get a popup stating that LM is "Scanning...". I've hooked up a USB interface and opened a DALI traffic monitor, and I just get loads of "framing error" messages on the traffic. This stops as soon LM stops scanning.
By using the USB interface and the software "DALI Cockpit" I am perfectly able to scan for devices and control the lights. However, as soon as I try to scan with LM, I get this framing error. I've tried to communicate through scripts, but I only get "timeout" when doing that.
The weird thing is that as late as yesterday, I had test-bench at home with one of the lamps and the same components as I did at the actual site. Wired up the same way, same components, no trouble. I found the 1 device I had connected and was able to control the lamp through scripts.
I googled "DALI framing error" and got a PDF from ABB stating that a "framing error" appears on their devices whenever a duplicate address is found. So I tried to disconnect every single lamp from the DALI circuit, but still I got the "framing error". I tried only connecting one lamp. Same thing.
What can I try to get this working again?
Image of LogicMachine scanning and the DALI traffic monitor:
First, run "Scan gateways" and see if the RS485 gateway is still there. If it appears in the list then try testing again with a single ballast and see if works. If it does not appear it's possible the it is damaged and must be replaced.
Another thing to try is to send a broadcast arc command from a script to check whether you can control ballasts this way or not.
(21.09.2021, 06:15)admin Wrote: First, run "Scan gateways" and see if the RS485 gateway is still there. If it appears in the list then try testing again with a single ballast and see if works. If it does not appear it's possible the it is damaged and must be replaced.
Thanks for your reply. I always find the gateway I expect, so it's in the list.
I ran this script:
require 'user.dali' res, err = dalicmd(0, 'arc', { addrtype = 'broadcast', value = 0 }) log(res, err)
What came back was:
dali_test 21.09.2021 12:24:34 * arg: 1   * nil * arg: 2   * string: timeout
I've now tried the following:
  • Deleting the `user.dali` script and rebooting. The script re-appears as expected, but still does not work.
  • Use another RS485 port on the LM5. The gateway appears after changing the port in the DALI tab, but still can't find any lamps or control them by scripts.
I have another LM5 with me, so I'll now be trying to replace the other one.
Edit: After swapping the LM5s, I'm still getting a framing error on the network and no devices appear in the device list. Could the DALI gateway be broken? I bought it in July and it's only been used at home for testing one lamp for this project. I can write new gateway ID to the gateway, the LED is on when i press the button on it. It appears to be fine from the outside.
I don't see any other option apart from replacing the RS485 gateway.
(22.09.2021, 12:48)admin Wrote: I don't see any other option apart from replacing the RS485 gateway.
As I mentioned, it's only two months old. Will I get a replacement on warranty? I've arranged with my vendor to order a new one pending the result of this thread, as it's important to get the site up and running. Can they ship the defective gateway back to you?
I see no problem in getting a replacement. It will be easier to sort this out via e-mail.