This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus profiles examples
#41
Try first reading via Read test. If it works try using this
https://forum.logicmachine.net/showthrea...+generator
------------------------------
Ctrl+F5
Reply
#42
Hello everyone,

does anybody have the profile for the energymeter from ABB (B24 112-100)?

I can´t get it to work. Thanky you!
Reply
#43
@tthamm, do you have the communication working via read test? The device documentation is very clear, you only have to convert addresses from hex to decimal for testing.

Try reading Active import with these settings:
- Function: Holding register (#3)
- Address: 20480
- Data type: uint64
- Read swap: Word
The read value is in 0.01KWh. If the value is incorrect then try using different read swap modes.
Reply
#44
(10.01.2022, 08:07)admin Wrote: @tthamm, do you have the communication working via read test? The device documentation is very clear, you only have to convert addresses from hex to decimal for testing.

Try reading Active import with these settings:
- Function: Holding register (#3)
- Address: 20480
- Data type: uint64
- Read swap: Word
The read value is in 0.01KWh. If the value is incorrect then try using different read swap modes.

@admin, thank you. i always get a "Operation timed out". The Logicmachine have D0, D1 and C. The Abb have A, B, C, i connect D0 = A, D1 = B, C = 0V. Is this correct?
Reply
#45
LM does not have D0/D1 markings, but A/B/GND. A is positive, B is negative. Try swapping A/B lines and also check that the serial port settings match.
Reply
#46
Hi,

I am trying to connect a Radiant Condesing Boiler to a LM via modbus.
I can read almost every value but i am stuck trying to control it.

Can someone help?

Attached the modus manual
.pdf   MODBUS_BRIDGE_INTF_PROTOCOL_L_00.pdf (Size: 628.07 KB / Downloads: 34)


Thank you in advance
Reply
#47
What is your profile?
PS. You should create separate thread for this.
------------------------------
Ctrl+F5
Reply
#48
(31.01.2022, 08:41)Daniel Wrote: What is your profile?
PS. You should create separate thread for this.

Hi Daniel,
Figure it out using bit mask.
Sorry for the of topic.
Reply
#49
Hi All,

Does anyone have a profile for ABB M4M 20 Meter?

M4M 20 MODBUS | ABB

I am currently working on profiles for:
Breathing Buildings NVHR
Condair Dehumidifer
Lindab HRU
RED Air Source Heat Pump
Daikin AC/VAM with RTS-Net modbus interface.

If anyone has profiles for these can you please post.  If not i will post when finished.

Many Thanks
Reply
#50
Hi,

When using a profile and reading blocs of parameters, "read_count" refers to number of 16bit modbus registers or number of registers defined on "datatype"?

I mean if I use something like this:

{"name": "Input_Register_1",
"bus_datatype": "float32",
"type": "inputregister",
"datatype": "float32",
"address": 4,
"read_offset": 0,
"read_count": 4,
"writable": 0,
"value_delta": 1,
"value_multiplier": 1,
"units": "%"
},
{"name": "Input_Register_2",
"bus_datatype": "float32",
"type": "inputregister",
"datatype": "float32",
"address": 4,
"read_offset": 2,
"read_count": 4,
"writable": 0,
"value_delta": 1,
"value_multiplier": 1,
"units": "%"
}


Is this reading input register 4 as 32bit float and register 6 as 32bit float using a single modbus read command? (count is 4 because we're reading registers 4,5,6 and 7)

Or should I define read_count as 2 because I'm reading 2 32bit registers?

Thanks.
Reply
#51
Size is always 1 register (16 bits) no matter what the data type is. The system will read the required number of registers based on the data type chosen.

Block read is needed for certain devices that don't allow reading registers directly but only via a large block read. Block read can be useful in large projects since it speeds things up but usually values can be simply read one by one.

See this example on how it should be specified correctly: https://forum.logicmachine.net/showthrea...4#pid21834
Reply
#52
(23.03.2022, 14:41)admin Wrote: Size is always 1 register (16 bits) no matter what the data type is. The system will read the required number of registers based on the data type chosen.

Block read is needed for certain devices that don't allow reading registers directly but only via a large block read. Block read can be useful in large projects since it speeds things up but usually values can be simply read one by one.

See this example on how it should be specified correctly: https://forum.logicmachine.net/showthrea...4#pid21834

Ok, thanks for your answer!!
Reply
#53
hello every body 
I have GenSet Deep sea Generator PLC, I read the registers. but I have a challenge reading the alarms 
Note:  I am using JSON Profile.

see attached image (Note: Updated)

Attached Files Thumbnail(s)
   
Best Regards,
Reply
#54
Check this example with bitmask, you have to use the same
https://forum.logicmachine.net/showthrea...9#pid25349
------------------------------
Ctrl+F5
Reply
#55
You can use Windows calculator for bitmasks. Switch to "Programmer" mode then switch keypad to "Bit toggling" mode. Switch required bits from 0 to 1. The HEX or DEC value will be your bitmask. For HEX you need to add 0x before the number in the profile (for example F becomes 0xF and so on).
Reply
#56
Thank You very much @Daniel and Admin
Best Regards,
Reply
#57
Hi,

When creating a json file, is there a field i can use to add that can be used to write to bus. See image?
   
Reply
#58
You can add "bus_write": true to the mapping entry to achieve this.
Reply
#59
(24.01.2022, 07:14)admin Wrote: LM does not have D0/D1 markings, but A/B/GND. A is positive, B is negative. Try swapping A/B lines and also check that the serial port settings match.

now the communikation works!

I´ve found the manufactur manual with chapter 9 (Communication with Modbus) inside.

Here are the fields: Quantity, Details, Start reg (hex), Size, Res., Unit, Data type,

for Example:

Quantity: Active import, Details: Tariff 1, Start reg (hex): 5170, Size: 4, Res.: 0,01, Unit: kWh, Data type: Unsigned

When i try reading Active import with these settings:
- Function: Holding register (#3)
- Address: 20480
- Data type: uint64
- Read swap: Word

the Answer is 94425 (i think its 944,25 kWh), that is correct.

but how i have to "translate" for the Logicmachine? I know, that i have to calculate hex into dec (like 5000 in hex is 20480 in dec). In the Modbus Profile Generater are Fields like bus_datatype, datatype, value_custom, read_swap...

Can you give me an example? Thankx
Reply
#60
Try this:
Code:
{   
      "bus_datatype": "int64",
      "address": 20480,
      "type": "register",
      "units": "kWh",
      "value_multiplier": 0.01,
      "name": "Active import",
      "datatype": "uint64"
    },
Try using profile generator if this is simpler.
https://forum.logicmachine.net/showthrea...8#pid19678
------------------------------