Log / Unlog Objects via script
Please, is there any way to turn on the log function of some objects via a tag and scheduled script?
I want to log some presence between 00:00 and 07:00, one of them is detecting a wrong motion at that time, and I don't want to log all  the presences  the whole day because I will get a lot of unnecessary data
Create two scheduled scripts that run at 0:00 and 7:00. Change group address as needed.
grp.create({ address = '0/0/1', log = true })
grp.create({ address = '0/0/1', log = false })
(11.08.2022, 06:27)admin Wrote: Create two scheduled scripts that run at 0:00 and 7:00. Change group address as needed.
Thank you
y = grp.getvalue('32/1/7')
x = grp.tag('Aufzeichnung')
m = #(x)
test = x[1].address
t = '32/1/8' -- TEST
log(m,y,test,t)
if y == true then
  u = 99 -- if log 99 then if was successfull
    for i = 1,m,1 do
    z = x[1].address --
    grp.create({ address = '32/1/6', log = true })--works
    grp.create({ address = z, log = true })--doesnt work
    log(z,u)
  u = 77 -- if log 77 then if wasnt successfull
      for i = 0,m,1 do
      grp.create({ address = x[i].address, log = false })
One quick question. Why does the first line of grp.create work and the second doesnt? Do i need to Convert the variable z to something else then string?
I want to change alot of Objects that all got the same tags.
-- F.Braun
Use an event script instead of resident:
enabled = event.getvalue()
objs = grp.tag('Aufzeichnung')
for _, obj in ipairs(objs) do
  grp.create({
    address = obj.address,
    log = enabled
Thank you!
-- F.Braun