This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

grp.write not on KNX TP
#1
Hi,
I am using the grp.write command in a script to update a boolean.
In the script i use grp.write('1/1/2', true, dt.bool)
The script is triggered by a change in value (another groupaddres) and the script is being triggered (added some log-commands to see what is happening).
The grp.write-command is being executed but is not visible on the groupmonitor (ETS through LM) and nothing happens.
When changing the boolean-value in de objects-tab of the LM it is being send to KNX-TP and shows up in the ETS groupmonitor.
I am not using any filtering on the LM (IP-TP or TP-IP).
Any idea what can cause this? (probably something stupid i guess)
Thanks,
Bart
Reply
#2
Which FW version are you running?
Reply
#3
(30.01.2017, 12:58)admin Wrote: Which FW version are you running?

I need to check tonight at home - it is the LM5p-PMU you shipped to me early jan2017. So i guess it must be running the latest FW?

Reply
#4
(30.01.2017, 13:07)bmodeco Wrote:
(30.01.2017, 12:58)admin Wrote: Which FW version are you running?

I need to check tonight at home - it is the LM5p-PMU you shipped to me early jan2017. So i guess it must be running the latest FW?


The firmware is the latest is guess 20170105.
I removed the script and copied it into a new one (doing the same thing) and now it is working.
Reply