16.10.2023, 12:29
Press scan selected
------------------------------
Ctrl+F5
Ctrl+F5
scripting
|
16.10.2023, 12:38
Go to System config - Netwotk - BAcnet Settings and de-select: Server enabled
Save and scan again
------------------------------
Ctrl+F5
16.10.2023, 12:50
16.10.2023, 12:57
Post your full script.
16.10.2023, 13:11
Use 'positive integer value' instead of 'analog value'. You can't write true / false to an integer value, try using 1 and 0 instead.
16.10.2023, 13:17
(16.10.2023, 13:11)admin Wrote: Use 'positive integer value' instead of 'analog value'. You can't write true / false to an integer value, try using 1 and 0 instead. done still not working
16.10.2023, 13:22
Use 'positive integer value' instead of 'analog value'.
------------------------------
Ctrl+F5
16.10.2023, 13:25
16.10.2023, 14:03
Use YABE(bacnet client software on PC) and check what values this objects actually allows and if it works from yabe.
------------------------------
Ctrl+F5 (16.10.2023, 14:03)Daniel Wrote: Use YABE(bacnet client software on PC) and check what values this objects actually allows and if it works from yabe. Sorry But I thing you getting what i'm trying to say I need Script that control Casambi Curtain from Logic Machine Beacause we are not getting proper or right script. If you can then please send me script.
17.10.2023, 11:58
If we don’t know how your BACnet environment looks like we cannot say anything why the script is not working, if you can do a discovery with YABE and show us how the datapoints in the BACnet device 400001 looks like then we might be able to help you further, just calling out you need a script won’t get you any further as we don’t have all the details …
|