ModBus Idegis DOM-24 can´t write
Hello, i have a problem with An Idegis equipment DOM-24. I can read all without problem but it is imposible to write to it.
This is the mapping
  "manufacturer": "Idegis",
  "description": "Dom-24",
  "mapping": [
    { "name": "Alarma Caudal", "bus_datatype": "bool", "type": "discreteinput", "address": 16 },
    { "name": "Alarma Baja salinidad", "bus_datatype": "bool", "type": "discreteinput", "address": 17 },
    { "name": "Alarma Alta salinidad", "bus_datatype": "bool", "type": "discreteinput", "address": 18 },
    { "name": "Alarma Celula de electrolisis", "bus_datatype": "bool", "type": "discreteinput", "address": 19 },
    { "name": "Alarma pH bajo", "bus_datatype": "bool", "type": "discreteinput", "address": 20 },
    { "name": "Alarma pH alto", "bus_datatype": "bool", "type": "discreteinput", "address": 21 },
    { "name": "Alarma Sobredosis min pH", "bus_datatype": "bool", "type": "discreteinput", "address": 23 },
    { "name": "Alarma Valor ORP bajo", "bus_datatype": "bool", "type": "discreteinput", "address": 24 },
    { "name": "Alarma Valor ORP alto", "bus_datatype": "bool", "type": "discreteinput", "address": 25 },
    { "name": "Alarma Valor Cloro bajo", "bus_datatype": "bool", "type": "discreteinput", "address": 26 },
    { "name": "Alarma Valor Cloro alto", "bus_datatype": "bool", "type": "discreteinput", "address": 27 },
    { "name": "Producción de Cloro", "bus_datatype": "uint16", "type": "inputregister", "address": 5, "units": "g/h" },
    { "name": "Producción", "bus_datatype": "uint16", "type": "inputregister", "address": 6, "units": "%" },
    { "name": "Consigna Producción", "bus_datatype": "uint16", "type": "inputregister", "address": 7, "units": "%" },
    { "name": "Resulta test de sal", "bus_datatype": "uint16", "type": "inputregister", "address": 8, "units": "mV" },
    { "name": "Consigna producción W", "bus_datatype": "uint16", "type": "register", "address": 38, "writeable":true, "write_multiple":true}
The last line is where is the problem. I don`t know what is wrong?
the desciption of the Idegis only allows to write multiple coil and multiple register.
.pdf   IDEGIS modbus v1.3.0 ES.pdf (Size: 408.31 KB / Downloads: 7)
Incorrect spelling: field name must be writable not writeable
(04.12.2023, 12:54)admin Wrote: Incorrect spelling: field name must be writable not writeable
Uffff, sorry...Thankyou,,but do the same...imposible to write...some idea?
  "mapping": [
    { "name": "Consigna producción W", "bus_datatype": "uint16", "type": "register", "address": 38, "writable":true, "write_multiple":true}
Did you delete device and add it again after uploading new profile?
(13.12.2023, 13:09)Daniel Wrote: Did you delete device and add it again after uploading new profile?
Yes. i do.
Can't really check manuals as they in Spanish, are sure write multiple is necessary?
(13.12.2023, 13:55)Daniel Wrote: Can't really check manuals as they in Spanish, are sure write multiple is necessary?
i translate the manual. In the  Supported Features it is only posible to write multiple.
.pdf   IDEGIS modbus v1.3.0 EN.pdf (Size: 1.24 MB / Downloads: 5)
Can you read this register correctly?
Yes the read funtion is correct
You didn't specify datatype, try uint16
Yes it was the problem, now work correctly. Thank you very much..