This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LSS100200 and Bacnet or Modbus TCP
#1
Hi, 

I have 10 LSS100200 on the site, and need to collect data from them to SCADA system. SCADA does support Modbus TCP and BACNET. 
Initially, project designers choose BACNET to collect data from LSS100200. This was tested by me and fine works, just need to put "Export" checkbox and SCADA reads and writes the data.

But now I need two of LSS100200 devices to communicate to Mitsubishi BACNET gateway for freon systems. As far as I learnt from this forum, it is not possible to use at the same time both Bacnet client and server in LSS100200.

Which options do I have to communicate at the same time with SCADA and BACNET gateway? Can I implement Modbus TCP Server (for SCADA) and Bacnet client for Mitsubishi at the same time?
Reply
#2
On LM you can do both Smile
Modbus client https://kb.logicmachine.net/integration/...tcp-slave/
------------------------------
Ctrl+F5
Reply
#3
(22.01.2024, 08:29)Daniel Wrote: On LM you can do both Smile
Modbus client https://kb.logicmachine.net/integration/...tcp-slave/

Thanks, Daniel. I tested, it works. Modbus Poll reads and writes ok.

By the way, do you know for SE, is there newer version of BACnet client? I have some old one, and cannot download from app store as it is banned for my country.

   
Reply
#4
SE has same version on its server.
------------------------------
Ctrl+F5
Reply