This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus script problem - Timeout
#1
Hi!

I'm facing some problems with modbus script over some time.
After some time (about week or two) communication goes to timeout (all reading/writing parameters). After I disable modbus script, enabling port on modbus tab, going to scan modbus devices on specific port (and system finds device with address), disable port on modbus tab, enable script again - everything starts to work again via script.

I attach code in here.
What can cause this?

Resident script with 10s sleep
Mitsubishi frequency converter
Code:
12345678910111213141516171819202122232425262728293031323334353637383940414243444546474849505152535455565758596061626364656667
require('luamodbus') vent_command = grp.getvalue('1/3/13') reset_command = grp.getvalue('34/1/4') control_motor = true motor_on = vent_command speed_value_perc = grp.getvalue('34/1/2') hz_sp = math.floor(speed_value_perc*50) mb = luamodbus.rtu() mb:open('/dev/RS485-2', 19200, 'E', 8, 1) mb:connect() mb:setslave(5) speed_read,err= mb:readregisters(202) --log('Speed read22',speed_read,err) read_mode,err= mb:readregisters(8) --log('Read mode',read_mode,err) read_speed,err= mb:readregisters(13) log('Read speed',read_speed,err) read_inputs,err= mb:readregisters(214) --log('Read inputs',read_inputs,err) read_alarm,err= mb:readregisters(500) --log('Read alarms',read_alarm,err) if control_motor then   if motor_on then     if read_mode ~= 75 then       res,err = mb:writeregisters(8,2)       --log('Write_motor_to_on',res,err)     end     if read_speed ~=hz_sp then       res,err =mb:writeregisters(13,hz_sp)       --log('Write_motor speed',res,err)     end   else     if read_mode ~= 0 then       res,err = mb:writeregisters(8,0)       --log('Write motor off',res,err)     end   end end if reset_command then   --log('Reseting frequency converter')   log(mb:writeregisters(1,1))   grp.checkupdate('34/1/4', 0) end mb:close() if read_mode == 75 or read_mode == 67 then   grp.update('34/1/3', read_speed/50) elseif read_mode == 0 then   grp.update('34/1/3', 0) end

I have seen this kind of problem with some other devices as well (chiller cooling units and swegon ventilation unit).
Reply
#2
Try adding mb:flush() after setslave.
Why don't you use profile?
------------------------------
Ctrl+F5
Reply
#3
Thanks!
Gonna try that.

One reason is that I like coding and I usually have custom projects where modbus part is custom every time.
To create profile and test it is quite time consuming compared with coding.