Script Guidance - Auto / On / Off, Lux Condition
Looking to script a setup that includes the following, any guidance appreciated...
Mode 0/0/1 -> Off (0) / Auto (127) / On (255) group address (with level noted in brackets).
Lux 0/0/2 -> from brightness sensor.
Setpoint 0/0/3 -> group address set via LM interface.
Output or Lights 0/0/4 -> group address for relay or dimmer etc.
Delay in seconds -> variable set above script.
Function/Script:
When Mode at 'Off' level (0), turn Output Off.
When Mode at 'Auto' level (127) it contentiously loops with comparing Setpoint to Lux group address...
  When Lux below Setpoint, Output group immediately On if Output currently Off.
  When Lux above Setpoint, after a Delay if Setpoint continues to stay above Lux, Output group Off if Output currently On.
When Mode at 'On' level (255), turn Output On.
Thank you
Hello
Here will be two event scripts
first - mode script
local mode = event.getvalue()
local output_addr = '0/0/4'
if mode == 0 then
  grp.write(output_addr, false)
elseif mode == 255 then
  grp.write(output_addr, true)
second - lux script
local lux = event.getvalue()
local delay = 3 -- seconds
local mode_addr = '0/0/1'
local lux_addr = '0/0/2'
local setpoint_addr = '0/0/3'
local mode = grp.getvalue(mode_addr)
local setpoint_lux = grp.getvalue(setpoint_addr)
if mode == 127 then
  if lux < setpoint_lux then
  elseif lux > setpoint_lux then
    os.sleep(delay)
    lux = grp.getvalue(lux_addr)
      grp.checkwrite(output_addr, false)
Thanks, that looks quite concise.
Is it difficult to script it so the delay starts again whenever the Lux drops below the Setpoint?
Do you mean something like this?
local mode_addr = '49/1/1'
local lux_addr = '49/1/2'
local setpoint_addr = '49/1/3'
local output_addr = '49/1/4'
if mode == 127 then
    os.sleep(delay)
    os.sleep(delay)