Trends API
#21
(17.06.2022, 13:23)admin Wrote: Not 120 but 127.0.0.1
You are right. The typo is only in the previous post, the address in the script is 127.0.0.1.
The error comes from having @ symbol in the password. It confuses the URL parser. Try using a password without @.
(17.06.2022, 13:30)admin Wrote: The error comes from having @ symbol in the password. It confuses the URL parser. Try using a password without @.
Yes, I saw that as well, so I have changed the password so that there is no @ any more.
I now get "timeout" in stead of "host not found"
The IP blocker might have blocked local access because of wrong password. Reboot the device and try again.
(17.06.2022, 13:34)admin Wrote: The IP blocker might have blocked local access because of wrong password. Reboot the device and try again.
I have also tried that. I actually down-powered it and repowered. Still same timeout.
What do you get logged from this script?
require('socket.http') log(socket.http.request('http://127.0.0.1/'))
(17.06.2022, 14:15)admin Wrote: What do you get logged from this script?
Here is the whole script:
require('json') require('socket.url') require('socket.http') user = 'admin' Password = 'Ringshusveien_18' tag = 'nyTrend' -- parameters daily = 365*24*60 -- 1 day daily1year = 365*24*12 -- 365 day daily2year = 2*365*24*12 -- 365 day year5_d = 5*365 -- 5 year obj = grp.tag(tag) for _, addr in ipairs(obj) do   object = addr.address   alias = addr.name   trend = {     object = knxlib.encodega(object), -- object id in db     name = alias, -- trend name     type = trend_type,     resolution = 5, -- every 5 minute     precision = 2, -- floating point precision     count_resolution = 365*24*12, -- 1 year     count_daily = 5*365 -- 5 years   }   data = json.encode(trend)   post = 'data=' .. socket.url.escape(data)   grp.removetags(addr.name, tag)   res, err = socket.http.request('http://' .. user .. ':' .. password .. '@127.0.0.1/scada-main/trends/save', post)   log(res, err) end script.disable(_SCRIPTNAME)
I am basically logging the result and errors from the saving of the trend.
Works for me. Try running script from my previous post and see what you get in Logs.
Your script is also missing trend_type variable. It should be either 'C', 'D' or 'G' (counter, counter with negative delta or absolute value respectively).
(19.02.2018, 15:39)Domoticatorino Wrote:
(07.12.2016, 20:15)Pawel Wrote: Thanks Erwin, those scripts save me a lot of time. I made a small change and all objects with specific tag will have own trend:
-- Batch adding trends - Created by Erwin van der Zwart - Schneider Electric Netherlands ----------- -- For spaceLYnk FW 1.2.1 or higher and homeLYnk FW 1.5.1 or higher -------------------------------- -- Refresh browser after creation to show the trends ----------------------------------------------- ----------------------------------------- Start Parameters ----------------------------------------- -- Create trend to object with this tag  tag_name = "make_trend" -- Set username and password for access to HL username = 'admin' password = 'admin' -- Select trend type to create (or multiple types on same object) create_trendtype_counter = true create_trendtype_counter_with_negative_delta = true create_trendtype_absolute_value = true -- Set trend precicion (!Important! Can only be these values: 0 to 8) trendprecision = 0 -- Set trend resolution (!Important! Can only be these values: 5 / 10 / 15 / 20 / 30 / 60 minutes)) trendresolution = 15 -- Set trend count resolution (!Important! Can only be these values: '30' = 30 days, '180' = 180 days, '365' = 1 year, '730' = 2 years, '1825' = 5 years trendcountresolution = 365 -- Set trend count days (!Important! Can only be these values: '1' = 1 year / '2' = 2 years / '5' = 5 years / '10' = 10 years) trendcountdaily = 10 -- Set show always 0 base line  trendshowzero = 0 -- 0 = disabled 1 = enabled ------------------------------------------ End Parameters ------------------------------------------ ------------------------------ DON'T CHANGE ANYTHING UNDER THIS LINE ------------------------------- -- Load modules require('json') require('socket.url') require('socket.http') -- Set HL ip address as localhost ip = '127.0.0.1' -- Create url for trend creation url = 'http://' .. username .. ':' .. password .. '@' .. ip .. '/scada-main/trends/save' -- Function to send request to create trend function url_send(trend_object, trend_name, trend_type, trend_resolution, trend_precision, trend_count_resolution, trend_count_daily, trend_show_zero, trend_id)   local trend = {       object = trend_object,       name = trend_name,       type = trend_type,       resolution = trend_resolution,       precision = trend_precision,     count_resolution = trend_count_resolution * 12 * 24, -- nr of days * nr of points in a hour at min resolution (60/5 = 12) * hours per day     count_daily = trend_count_daily * 365, -- nr of days * 365 days a year       show_zero = trend_show_zero,       id = trend_id,     }   data = json.encode(trend)     form_data = 'data=' .. socket.url.escape(data)     socket.http.TIMEOUT = 15        local res, code, response_header = socket.http.request(url, form_data)   return res, code, response_header end -- Set counters for creation log number_of_trends = 0 number_failed = 0 objectwithtag = grp.tag(tag_name) -- Loop for each group adress with specific tag  for key, value in pairs(objectwithtag) do      -- Get current group address from loop    current_GA = knxlib.decodega(value.id)      -- Get current object info   objectinfo = grp.find(current_GA)        -- Check if object excists   if objectinfo ~= nil then            -- Set parameters for request     trendobject = objectinfo.id     trendname = objectinfo.name     trendid = ''          -- Check if trend type 'Counter' should be created     if create_trendtype_counter == true then              -- Call function to send create request       result, code, response_header = url_send(trendobject, trendname, 'C', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)              -- Calculate results for creation results log         if result == '{"success":true}' then           number_of_trends = number_of_trends + 1         else           number_failed = number_failed + 1         end            end          -- Check if trend type 'Counter with negative delta' should be created     if create_trendtype_counter_with_negative_delta == true then                    -- Call function to send create request       result, code, response_header = url_send(trendobject, trendname, 'D', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)                  -- Calculate results for creation results log         if result == '{"success":true}' then           number_of_trends = number_of_trends + 1         else           number_failed = number_failed + 1         end            end          -- Check if trend type 'Absolute value' should be created     if create_trendtype_absolute_value == true then                    -- Call function to send create request       result, code, response_header = url_send(trendobject, trendname, 'G', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)                  -- Calculate results for creation results log         if result == '{"success":true}' then           number_of_trends = number_of_trends + 1         else           number_failed = number_failed + 1         end            end        end    end      if number_failed == 0 then     log ("Created " .. number_of_trends .. " trends succesfully") else     log ("Created " .. number_of_trends .. " trends succesfully and creation of " .. number_failed .. " trends failed") end -- Disable script when done automaticly script.disable(_SCRIPTNAME)
Hi Pawel,
in this case don't you create .csv file?
I have just carried out a test with this script which seems clear and complete to me. But it doesn't work for me?! I linked the Tag to three variables for the test and the log return is as follows: * string: Created 0 trends successfully and creation of 4 trends failed. Do you have any possible solutions?
Which controller and what firmware do you use?
(18.12.2024, 14:51)Daniel Wrote: Which controller and what firmware do you use?
Schneider LSS100200 (Spacelynk), firmware 3.0.0
Did you disable: Block unsafe functions in scripts: in general configuration?
(18.12.2024, 15:29)Daniel Wrote: Did you disable: Block unsafe functions in scripts: in general configuration?
I tried with and without the function, the result is the same.
Can you try this version, it uses webrequests instead of URL with basic authentication that is not supported anymore in FW 3.0.0
-- Batch adding trends v1.3 - Created by Erwin van der Zwart - Schneider Electric Netherlands ------------------- -- For spaceLYnk FW 3.0.0 or higher and Wiser for KNX FW 3.0.0 or higher ---------------------------------------- -- Make sure that "Block unsafe functions in scripts" is disbled in General Configuration -- Refresh browser after creation to show the trends ------------------------------------------------------------ ----------------------------------------------- Start Parameters ------------------------------------------------ -- Start address of objects start_objectaddress = '3/0/0' -- Trends for all objects between these range are created -- End address of objects end_objectaddress = '3/0/2' -- Select trend type to create (or multiple types on same object) create_trendtype_counter = false create_trendtype_counter_with_negative_delta = false create_trendtype_absolute_value = true -- Select aggregate function (!Important! Can only be these values: AVERAGE / MIN / MAX / LAST)) trendaggregatefunction = 'AVERAGE' -- Set trend resolution (!Important! Can only be these values: 5 / 10 / 15 / 20 / 30 / 60 minutes)) trendresolution = 5 -- Set trend precicion (!Important! Can only be these values: 0 to 8) decimal places trendprecision = 2 -- Set trend count resolution (!Important! Can only be these values: '30' = 30 days, '180' = 180 days, '365' = 1 year, '730' = 2 years, '1825' = 5 years trendcountresolution = 365 -- Set trend count days (!Important! Can only be these values: '1' = 1 year / '2' = 2 years / '5' = 5 years / '10' = 10 years) trendcountdaily = 10 -- Set show always 0 base line trendshowzero = 0 -- 0 = disabled 1 = enabled ------------------------------------------------ End Parameters ------------------------------------------------- ------------------------------------ DON'T CHANGE ANYTHING UNDER THIS LINE -------------------------------------- -- Calculate start address to DB format start_objectaddress = knxlib.encodega(start_objectaddress) -- Calculate end address to DB format end_objectaddress = knxlib.encodega(end_objectaddress) -- Function to send request (in this case to create a trend) function webrequest(mod, act, vars, data)   require('json')   require('dbenv')   local path   vars = vars or {}   function getvar(v)       return vars[ v ]   end   json.data = function()       return data or {}   end   if mod == 'plugin' then   path = 'plugins/' .. act .. '/web.lua'   else    path = 'web/' .. mod .. '/' .. act .. '.lua'   end   result = dofile('/lib/genohm-scada/' .. path)   -- Calculate results for creation results log   if result.success == true then     number_of_trends = number_of_trends + 1   else     number_failed = number_failed + 1   end end -- Function to create vars function createvars(trend_object, trend_name, trend_type, trend_aggregate_function, trend_resolution, trend_precision, trend_count_resolution, trend_count_daily, trend_show_zero, trend_id)   local vars = {       object = trend_object,       name = trend_name,       type = trend_type,       aggregation = trend_aggregate_function,       resolution = trend_resolution,       precision = trend_precision,     count_resolution = trend_count_resolution * 12 * 24, -- nr of days * nr of points in a hour at min resolution (60/5 = 12) * hours per day     count_daily = trend_count_daily * 365, -- nr of days * 365 days a year       show_zero = trend_show_zero,       id = trend_id,     }   return vars end -- Set counters for creation log number_of_trends = 0 number_failed = 0 -- Loop from startadres to end address to create trends for i = start_objectaddress, end_objectaddress, 1 do     -- Get current group address from loop   current_GA = knxlib.decodega(i)     -- Get current object info   objectinfo = grp.find(current_GA)        -- Check if object excists   if objectinfo ~= nil then            -- Set parameters for request     trendobject = objectinfo.id     trendname = objectinfo.name     trendid = ''         -- Check if trend type 'Counter' should be created     if create_trendtype_counter == true then       -- Call function to create vars       requestdata = createvars(trendobject, trendname, 'C', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)       webrequest('trends', 'save', {request = 'save'}, requestdata)     end         -- Check if trend type 'Counter with negative delta' should be created     if create_trendtype_counter_with_negative_delta == true then             -- Call function to send create vars       requestdata = createvars(trendobject, trendname, 'D', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)       webrequest('trends', 'save', {request = 'save'}, requestdata)     end         -- Check if trend type 'Absolute value' should be created     if create_trendtype_absolute_value == true then             -- Call function to send create vars       requestdata = createvars(trendobject, trendname, 'G', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)       webrequest('trends', 'save', {request = 'save'}, requestdata)     end       end   end     if number_failed == 0 then     log ("Created " .. number_of_trends .. " trends succesfully") else     log ("Created " .. number_of_trends .. " trends succesfully and creation of " .. number_failed .. " trends failed") end -- Disable script when done automaticly script.disable(_SCRIPTNAME)
(19.12.2024, 14:57)Erwin van der Zwart Wrote: Can you try this version, it uses webrequests instead of URL with basic authentication that is not supported anymore in FW 3.0.0
It works perfectly!  thank you very much for the time saved on creating the graphics Smile
Is there not a way to use the trends lua library to create trends in the script? I'm creating a utility app, where quickly adding trends is one functionality. I don't want users of that app to require filling in their username and password to run behind-the-scenes http requests.
If I put this inside a script:
require 'trends' log(trends) log(trends.create)
Then it's clear that there is a create function inside the library. It's unfortunately not possible for me to determine what the parameters for that function is. Could you document which parameters are required to use that create function? Maybe even add that to the documentation.
Sorry if hijacking this post was wrong. Thought it best to continue with the existing issue, since it's quite similar.
I tried adding new trends directly through the database, but then I get errors about the trend file not existing, which I assume your backend creates when users submit through the normal form.
Edit:
I tried using a variation of these arguments, which logs an empty string and no errors. Though, the trend is not added. The arguments are based on the database column names.
log(trends.create('Test', {     name = 'Test',     type = 'G',     aggregation = 'MAX',     object = 53516,     precision = 0,     resolution = 15,     count_resolution = 51840,     count_daily = 730,     show_zero = 0,     sortorder = 1,     created = 1632087317,     category = 'Test', }))
Use webrequests: https://forum.logicmachine.net/showthrea...7#pid37437