This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus Connection ATV320
#1
Hello all,

 i try to connect an ATV320 Variable speed drive from schneider electric with modbus connection. 
I've made many settings but it's impossible for me to connect it to the LM.

In the LM, i activate the modbus RTU. i set the speed at 19200bps  like the ATV 

In the ATV I enable the modbus i set the adress to 1 but  i don't what i need to choose in this settings 


if some one can help me 
THX

Attached Files Thumbnail(s)
   
Reply
#2
Choose Even in Parity settings.
Reply
#3
(24.12.2024, 13:51)admin Wrote: Choose Even in Parity settings.
THX Admin 
I made this but not connection when i made a RTU scan or a Read test

Attached Files Thumbnail(s)
   
Reply
#4
Try swapping RS485 A/B and make sure that GND is connected between LM and Modbus device.
Reply
#5
(24.12.2024, 14:09)admin Wrote: Try swapping RS485 A/B and make sure that GND is connected between LM and Modbus device.

I switched the drive off and on again and now it works.

Thanks for your help Admin