Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
(10.03.2018, 17:16)buuuudzik Wrote: (10.03.2018, 17:14)Domoticatorino Wrote: It is a Schneider HL 2.0.1
I mean updated version of above script I've adjusted it to be more universal, added new variables:
Code: valveStatesTag = 'circulation_pump'
pumpGA = '1/1/10'
openingValveTime = 300 -- time for fully open the valve (maximum time for next calculation)
minInterval = 30 -- minimum offset for next calculation
opened, firstTimestamp = false, 0
valveStates = grp.tag(valveStatesTag)
for v = 1, #valveStates, 1 do
valveState = valveStates[v]
if valveState.value then
opened = true
if firstTimestamp > 0 then
if firstTimestamp > valveState.updatetime then firstTimestamp = valveState.updatetime end
else
firstTimestamp = valveState.updatetime
end
end
end
if opened then
fullyOpened = (os.microtime() - firstTimestamp) >= openingValveTime
if fullyOpened then
grp.checkwrite(pumpGA, true)
nextCalculationAfter = minInterval
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1 - (os.microtime() - firstTimestamp) -- run a little after possible change
end
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1
end
log('Next calculation after: ' .. nextCalculationAfter .. 's.')
os.sleep(nextCalculationAfter)
No, it does not work.
there is not any mistake and any error log. Is there the opportunity to have a debug for lua?
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
What are your settings? It is resident script 0s? Did you tried disable and enable script? Did you add the tag to valves? Do you changed the GA for pump?
When script start it should log such message in the Logs:
Code: Circulation pump calculation 10.03.2018 18:33:49
* string: Next calculation after: 293s.
Done is better than perfect
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
It is a resident script set at 60 seconds.
Obviously I add tag and change address of pump. In the log I read "next calculation after" but pumps does not start.
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
(10.03.2018, 18:36)Domoticatorino Wrote: It is a resident script set at 60 seconds.
Obviously I add tag and change address of pump. In the log I read "next calculation after" but pumps does not start.
Please change the time to 0, update script to the newest version, disable and enable it and it must work.
I've checked it and all works perfect. You can also comment this line with log.
Done is better than perfect
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
Thank you very much. It works!!
Great
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
Code: valveStatesTagEstate = 'pompa_circolazione_giorno_estate'
valveStatesTagInverno = 'pompa_circolazione_giorno_inverno'
pumpGA = '2/0/1'
openingValveTime = 60 -- time for fully open the valve (maximum time for next calculation)
minInterval = 30 -- minimum offset for next calculation
opened, firstTimestamp = false, 0
if stagione == false then
valveStatesEstate = grp.tag(valveStatesTagEstate)
for v = 1, #valveStatesEstate, 1 do
valveStateEstate = valveStatesEstate[v]
if valveStateEstate.value then
opened = true
if firstTimestamp > 0 then
if firstTimestamp > valveStateEstate.updatetime then firstTimestamp = valveStateEstate.updatetime end
else
firstTimestamp = valveStateEstate.updatetime
end
end
end
else
valveStatesInverno = grp.tag(valveStatesTagInverno)
for v = 1, #valveStatesInverno, 1 do
valveStateInverno = valveStatesInverno[v]
if valveStateInverno.value then
opened = true
if firstTimestamp > 0 then
if firstTimestamp > valveStateInverno.updatetime then firstTimestamp = valveStateInverno.updatetime end
else
firstTimestamp = valveStateInverno.updatetime
end
end
end
end
if opened then
fullyOpened = (os.microtime() - firstTimestamp) >= openingValveTime
if fullyOpened then
grp.checkwrite(pumpGA, true)
nextCalculationAfter = minInterval
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1 - (os.microtime() - firstTimestamp) -- run a little after possible change
end
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1
end
-- log('Next calculation after: ' .. nextCalculationAfter .. 's.')
log(valveStatesEstate)
os.sleep(nextCalculationAfter)
Hi,
In your opinion what is wrong in this script above. I add a condition to separate winter condition from summer condition.
I log variable log(valveStatesEstate) but the result is nil. Objects tags are correct and in other 2 scripts (the same) everything works fine.
I cannot understand the reason why it does not working. I expect to read TRUE in log (valveStateEstate).
Thank you for your help.
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
You are trying to log value 'ValveStatesEstate' but you hasn't defined stagione so stagione equals nil so else condition is executed.
But generally when you extend this script maybe better would be create some function and do script more elastic also for the future
See below (but still you must define stagione!):
Code: valveStatesTagEstate = 'pompa_circolazione_giorno_estate'
valveStatesTagInverno = 'pompa_circolazione_giorno_inverno'
pumpGA = '2/0/1'
openingValveTime = 60 -- time for fully open the valve (maximum time for next calculation)
minInterval = 30 -- minimum offset for next calculation
opened, firstTimestamp = false, 0
function getParamsFromValveStates(valvesTag)
local valveStates = grp.tag(valveStatesTag)
for v = 1, #valveStates, 1 do
valveState = valveStates[v]
if valveState.value then
opened = true
if firstTimestamp > 0 then
if firstTimestamp > valveState.updatetime then firstTimestamp = valveState.updatetime end
else
firstTimestamp = valveState.updatetime
end
end
end
return opened, firstTimestamp
end
if not stagione then opened, firstTimestamp = getParamsFromValveStates(valveStatesTagEstate)
else opened, firstTimestamp = getParamsFromValveStates(valveStatesTagInverno) end
if opened then
fullyOpened = (os.microtime() - firstTimestamp) >= openingValveTime
if fullyOpened then
grp.checkwrite(pumpGA, true)
nextCalculationAfter = minInterval
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1 - (os.microtime() - firstTimestamp) -- run a little after possible change
end
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1
end
-- log('Next calculation after: ' .. nextCalculationAfter .. 's.')
os.sleep(nextCalculationAfter)
Done is better than perfect
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
(24.04.2018, 17:03)buuuudzik Wrote: You are trying to log value 'ValveStatesEstate' but you hasn't defined stagione so stagione equals nil so else condition is executed.
But generally when you extend this script maybe better would be create some function and do script more elastic also for the future
See below (but still you must define stagione!):
Code: valveStatesTagEstate = 'pompa_circolazione_giorno_estate'
valveStatesTagInverno = 'pompa_circolazione_giorno_inverno'
pumpGA = '2/0/1'
openingValveTime = 60 -- time for fully open the valve (maximum time for next calculation)
minInterval = 30 -- minimum offset for next calculation
opened, firstTimestamp = false, 0
function getParamsFromValveStates(valvesTag)
local valveStates = grp.tag(valveStatesTag)
for v = 1, #valveStates, 1 do
valveState = valveStates[v]
if valveState.value then
opened = true
if firstTimestamp > 0 then
if firstTimestamp > valveState.updatetime then firstTimestamp = valveState.updatetime end
else
firstTimestamp = valveState.updatetime
end
end
end
return opened, firstTimestamp
end
if not stagione then opened, firstTimestamp = getParamsFromValveStates(valveStatesTagEstate)
else opened, firstTimestamp = getParamsFromValveStates(valveStatesTagInverno) end
if opened then
fullyOpened = (os.microtime() - firstTimestamp) >= openingValveTime
if fullyOpened then
grp.checkwrite(pumpGA, true)
nextCalculationAfter = minInterval
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1 - (os.microtime() - firstTimestamp) -- run a little after possible change
end
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1
end
-- log('Next calculation after: ' .. nextCalculationAfter .. 's.')
os.sleep(nextCalculationAfter)
Thank you very much...stupid mistake!! I have to hire you
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
Nice
Done is better than perfect
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
How long do you code Lua?
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
25.04.2018, 02:42
(This post was last modified: 25.04.2018, 02:44 by buuuudzik.)
(24.04.2018, 23:24)ODomoticatorino Wrote: How long do you code Lua?
3-4 years with Logic Machine. Sometimes less sometimes more. But I’ve asked a lot of questions also on this forum Now I like more Javascript than Lua and LM would be for me perfect with modern JS instead the Lua
Done is better than perfect
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
Wow cool. I am using LM for 2 years and I hope to improve my skills in coding.
You are very good. Thanks.
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
25.04.2018, 10:57
(This post was last modified: 25.04.2018, 10:57 by buuuudzik.)
For sure, be patient, try and ask
Done is better than perfect
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
Hi there,
I have a big problem with the script below. Please consider that I have 3 same script (obviosly with different varables) and everyting works fine. The one below does not work anymore.
I have seen in the obkect list that last update of group address 2/0/2 was dated 16th of September. The other correctly dated today. I cannot understand the reason why it does not work anymore. And nothing changed.
I tried to delate scritp and redo it without success. I tried to do again object 2/0/2 without success. Nothing group address 2/0/2 never update. Could you help me please?
Thanks.
Code: valveStatesTagEstate = 'pompa_circolazione_mansarda_estate'
valveStatesTagInverno = 'pompa_circolazione_mansarda_inverno'
stagione = grp.getvalue('2/0/100')
pumpGA = '2/0/2'
openingValveTime = 60 -- time for fully open the valve (maximum time for next calculation)
minInterval = 30 -- minimum offset for next calculation
opened, firstTimestamp = false, 0
if stagione == false then
valveStatesEstate = grp.tag(valveStatesTagEstate)
for v = 1, #valveStatesEstate, 1 do
valveStateEstate = valveStatesEstate[v]
if valveStateEstate.value then
opened = true
if firstTimestamp > 0 then
if firstTimestamp > valveStateEstate.updatetime then firstTimestamp = valveStateEstate.updatetime end
else
firstTimestamp = valveStateEstate.updatetime
end
end
end
else
valveStatesInverno = grp.tag(valveStatesTagInverno)
for v = 1, #valveStatesInverno, 1 do
valveStateInverno = valveStatesInverno[v]
if valveStateInverno.value then
opened = true
if firstTimestamp > 0 then
if firstTimestamp > valveStateInverno.updatetime then firstTimestamp = valveStateInverno.updatetime end
else
firstTimestamp = valveStateInverno.updatetime
end
end
end
end
if opened then
fullyOpened = (os.microtime() - firstTimestamp) >= openingValveTime
if fullyOpened then
grp.checkwrite(pumpGA, true)
nextCalculationAfter = minInterval
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1 - (os.microtime() - firstTimestamp) -- run a little after possible change
end
else
grp.checkwrite(pumpGA, false)
nextCalculationAfter = openingValveTime + 1
end
-- log('Next calculation after: ' .. nextCalculationAfter .. 's.')
os.sleep(nextCalculationAfter)
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
Add some logging to your script before any grp.checkwrite call. Since it uses grp.checkwrite there won't be any value sent unless it changes.
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
Ok, log of which variable? Thanks
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
Add this before os.sleep, this will give some info where the script is going:
Code: log(stagione, opened, os.time(), firstTimestamp)
Posts: 940
Threads: 161
Joined: Jul 2015
Reputation:
33
Please:
Maybe you have some error in tags.
Done is better than perfect
Posts: 400
Threads: 88
Joined: Jul 2016
Reputation:
3
(24.10.2018, 12:20)buuuudzik Wrote: Please:
Maybe you have some error in tags.
Here below the log:
Tesy_pompa_circolazione_mansarda 24.10.2018 14:36:47
* table:
[1]
* table:
[export]
* number: 0
[disablelog]
* number: 1
[tagcache]
* string: clima, pompa_circolazione_mansarda_inverno, pompa_circolazione_mansarda_estate
[datahex]
* string: 00
[units]
* string:
[value]
* bool: false
[comment]
* string:
[updatetime]
* number: 1540384570
[datatype]
* number: 1009
[address]
* string: 2/0/107
[id]
* number: 4203
[data]
* bool: false
[highpriolog]
* number: 0
[pollinterval]
* string:
[readoninit]
* number: 0
[name]
* string: T7 FB Elettrovalvola pavimento mansarda
[decoded]
* bool: true
[size=undefined]
Tesy_pompa_circolazione_mansarda 24.10.2018 14:36:47
* arg: 1
* bool: true
* arg: 2
* bool: false
* arg: 3
* number: 1540384607
* arg: 4
* number: 0[/size]
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
The last script you've posted does not have valveStates variable anywhere, please post the latest version that you are using. Also, try turning 2/0/107 on.
|