08.08.2018, 07:01
Do any have an example of how to mass greate virtual objects in json?
BR Even Sundgot.
BR Even Sundgot.
Json virtual object
08.08.2018, 07:01
Do any have an example of how to mass greate virtual objects in json? BR Even Sundgot.
08.08.2018, 07:16
Why not use a script with grp.create in a loop? What kind of objects do you want to create?
08.08.2018, 07:25
That`s probably just as good. Im doing some testing and want to create 200 objects like this:
BACnet_001 to BACnet_200 And I want them to start at 32\1\1 Datatype 1 Byte scale
08.08.2018, 07:49
Code: 12345678 for i = 1, 200 do
name = string.format('BACnet_%03d', i)
grp.create({
name = name,
address = '32/1/' .. i,
datatype = dt.scale,
08.08.2018, 07:54
08.08.2018, 10:33
Is there any way to add the same script to several objects, but with one thing changing everytime?
I have this script that i want to add to 200 objects, but the ID needs to be changed everytime. from 65793 to 65992 require('bacnet') value = event.getvalue() bacnet.write(127001, 'analog value', 65809, value)
08.08.2018, 10:49
You can attach event script to a tag. Use event.dstraw to calculate BACnet object id from the group address that triggered the script.
08.08.2018, 10:54
Can you give me an example of this?
08.08.2018, 11:00
First, add a certain tag to all objects via mass edit. Then create an event script which is mapped to the tag you've added. If your range is 32/1/1..32/1/200 then you don't need any extra conversion since it is 65793..65992 in numeric form.
Code: 12345 require('bacnet')
bacnet.write(127001, 'analog value', event.dstraw, value)
08.08.2018, 11:36
(08.08.2018, 11:00)admin Wrote: First, add a certain tag to all objects via mass edit. Then create an event script which is mapped to the tag you've added. If your range is 32/1/1..32/1/200 then you don't need any extra conversion since it is 65793..65992 in numeric form. I dont understand how, but it works! ![]() Thanks!
09.08.2018, 13:29
Is there any way to adjust this script to match the range 32/2/1 - 32/2/250 and 32/3/1 - 32/3/250 (all have the same Tag)
I have 500 objects that i want to link to ID 0- 500.
09.08.2018, 16:41
(09.08.2018, 13:29)Evens Wrote: Is there any way to adjust this script to match the range 32/2/1 - 32/2/250 and 32/3/1 - 32/3/250 (all have the same Tag) Nothing has to be modified it will work. your bacnet range will be 66049 - 66290 and 66305 - 66554
10.08.2018, 06:30
event.dstraw is an integer value of group address. You can easily convert to a 0..499 range like this:
Code: 123456789101112 id = event.dstraw
if 66049 <= id and id <= 66290 then
id = id - 66049
elseif 66305 <= id and id <= 66554 then
id = id - 66305 + 250
return
bacnet.write(127001, 'analog value', id, value)
10.08.2018, 08:37
Thanks!
I can’t get it to work properly. maybe I’m doing something wrong. How do you convert from Group Address to the number?
10.08.2018, 08:40
H/M/L
H * 2048 + M * 256 + L
10.08.2018, 08:52
Thanks!
This event.dstraw, do you have an easy explanation for it, I’d like to understand what it does.
10.08.2018, 09:28
event.dst is group address that triggered the script in H/M/L format, event.dstraw is the same address but in numeric form.
13.08.2018, 06:10
Thanks, Now i understand
