How prepare calculating of central statuses on Logic Machine by event-script and tags? E.g. "1Floor status", "Kitchen status" ...
Here are 2 functions for getting OR / AND values for binary objects with the same tag. You can then use the result to write out the status.
function tag_and(tag)   local objects, result   result = true   objects = grp.tag(tag)   for _, object in ipairs(objects) do     result = result and object.data   end   return result end function tag_or(tag)   local objects, result   result = false   objects = grp.tag(tag)   for _, object in ipairs(objects) do     result = result or object.data   end   return result end
(16.02.2016, 11:22)admin Wrote: Here are 2 functions for getting OR / AND values for binary objects with the same tag. You can then use the result to write out the status.
ThanksWink
Is there any solution to prevent executing this function on every tag change?
When there is 5 - 10 statuses, there is no problem, but if there is 100 or 200 statuses of whole house, script has to execute 100 time which can slow down LM...
(18.02.2016, 08:21)Pawel Wrote: Is there any solution to prevent executing this function on every tag change?
Before doing a function you can check if the status of this lamp is the same that the central status.
tag="kitchen" if status1~=central then tag_or(tag) end