25.11.2017, 18:06
I needed to send an email when an event with a group address occurs. Does anyone have an example?
Send e-mail
25.11.2017, 18:06
26.11.2017, 00:45
Just use the build in mail function and trigger it as event based script: Code: -- make sure mail settings are set in common functions library before using this function
subject = 'E-mail test'
message = 'Testing e-mail'
mail('user@example.com', subject, message)Erwin
27.11.2017, 10:15
27.11.2017, 10:29
I need to send a value from storage by email, someone has an example?
27.11.2017, 10:35
For event value you can use an event script:
Code: value = event.getvalue()
message = 'Event value is ' .. tostring(value)
mail('user@example.com', subject, message)For storage value you need a scheduled script. But, if you want to send a value on each storage value change you should use a virtual object instead because you cannot attach an event script to storage changes. Code: value = storage.get('myvalue')
message = 'Storage value is ' .. tostring(value)
27.11.2017, 10:42
Thank you very much
10.10.2021, 18:26
(This post was last modified: 10.10.2021, 20:02 by d.r soutras.)
Hello guys!
A little bit of help here.. I have cycling send from a GA that comes from a generator. Can we adjust the code to send the email only if the GA changes it’s state. So an email with subject ‘Generator On’ will be sent when the GA is 1 and an email with subject ‘Generator Off’ will be sent when the GA is 0. Thank you in advance!!
11.10.2021, 09:37
Something like that would do, event script
mydata = storage.get('myobjectdata', 2)
if value then
if value ~= mydata then
--emial for on
--email for off
storage.set('myobjectdata', value)
11.10.2021, 15:52
As always… your script works like a charm!!!!
Thank you very much!! |
« Next Oldest | Next Newest »