different value throughout the day
#21
You can simply put else because there are only two possible states. But a better solution is to use a scheduler with sunrise and sunset events instead of a fixed time.
(09.07.2023, 08:46)Erwin van der Zwart Wrote: elseif now.hour >= 22 and now.hour < 7 then…
This is impossible, a value can never be greater as 22 AND at the same time lower as 7 (:
Use: elseif now.hour >= 22 or now.hour < 7 then
Thanks for the info. The thing is that i want to send a 0 between 22:00 and 7:00 or even 7:30 , and between 7:30  and 22:00 a 1.
That's why i tried first in shedulers @ main object Day/Night and there 2 events for day 7:30 ON and other 22:00 OFF. But this doesn't seems to work for some reason.
You have mapped scheduler control and on/off to the same group address. Once scheduler sends off it turns itself off and you need to manually turn it on afterwards. Remove 10/0/2 from on/off object and it will work correctly.
(09.07.2023, 10:38)admin Wrote: You can simply put else because there are only two possible states. But a better solution is to use a scheduler with sunrise and sunset events instead of a fixed time.
Thanks for the replay. Just reacted to Erwin. The shedulers seems to be a better solution either, but with fixed times for the dressing room. This option is temporary because we don't have a door between the room and dressing, and when we go to the toilet at night, the lights are going on. For garden light, sunset and sunrise is a better option indeed.
(10.07.2023, 13:09)admin Wrote: You have mapped scheduler control and on/off to the same group address. Once scheduler sends off it turns itself off and you need to manually turn it on afterwards. Remove 10/0/2 from on/off object and it will work correctly.
Ok, great. It works not like a charm! Thank you a lot. Sometimes it's just a small thing that can make it difficult, especially when you are a starter