Shutter Lock signal
Hi.
I have a case where, as soon as anyone use the manual buttons for shutters i want to send a "1" to lock the automatic function in a shutter actuator
The objects is:
UP/DOWN 1bit (0/1)
STOP 1bit (0)
LOCK AUTOMATICS 1bit (1)
Is there a script that check an adress if it gets any kind of telegram even if it´s "1" or "0" and can send a "1" to a output..
Best regards
Hi.
Here is a simple script for your function.
value = grp.getvalue('1/1/1') -- upp/down adress
if value >= 0 or value <= 1 then
grp.write('1/1/2', 1) -- lock automatics
sorry, delete the group adress in the first line.
value = grp.getvalue()
then put the script in up/down object.
Since your UP/DOWN object is 1 bit and you don't care about the value there's no need for comparison.
Another point is that event.getvalue() should be used instead of grp.getvalue(). Since the return value for 1 bit objects is true/false then comparison with 0/1 will not work.
You just need one line in your script attached to UP/DOWN object, change 1/1/2 to your LOCK object address:
grp.write('1/1/2', true)
(11.05.2019, 18:46)Rauschentofft Wrote: Hi.
Hi.
Thank you for the help...
I think i got it to work with some small modefy
value = grp.getvalue() -- upp/down adress
if value == upp or value == down then
  grp.write('10/1/2', true) -- lock automatics
Best regards
Anders
(13.05.2019, 06:17)admin Wrote: Since your UP/DOWN object is 1 bit and you don't care about the value there's no need for comparison.
Is it so simple ??
It works but it does the same thing as just having one line:
Here's what your current script does:
value = grp.getvalue() - no address/name is passed to grp.getvalue(), so value is nil
if value == upp or value == down then - both upp and down are not defined so they are nil, so the actual comparison is if nil == nil or nil == nil then
Hi.
Best regards
Anders
Is it so simple ??
Ha ha.... Yes it´s working with that simple line, amazing... Smile
I also have a light color control via a template that the customer want´s to stop in the same way, if you use the manual dimming button, it must be possible
in the same type of script line ?!
//Anders