This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Shutter Lock signal
#3
Since your UP/DOWN object is 1 bit and you don't care about the value there's no need for comparison.

Another point is that event.getvalue() should be used instead of grp.getvalue(). Since the return value for 1 bit objects is true/false then comparison with 0/1 will not work.

You just need one line in your script attached to UP/DOWN object, change 1/1/2 to your LOCK object address:
Code:
grp.write('1/1/2', true)