Threads: 87
I am looking for a script that i can use to send a value every xx minutes.
Found this that could work. But this is once, and i need it to resend for example every 30 minutes to pulse an output.
Could anyone help me with such a script.
Code: -- group address or name
addr = '1/1/1'
-- find required object
obj = grp.find(addr)
-- object exists and current state is "on"
if obj and obj.data then
-- delta is in seconds
delta = os.time() - obj.updatetime
-- switch off when timer expires
if delta >= 50 * 60 then
grp.write(addr, false)
Threads: 8
Just create a resident script at 0 and insert this:
Code: grp.write('1/1/1', true)
os.sleep(1800)
Threads: 87
(06.04.2020, 21:34)Erwin van der Zwart Wrote: Hi,
os.sleep(1800)
That simple..
I need a 0 in between, so i duplicated the scripts. But after testing, i guess this is not the correct way.
Code: grp.write('32/1/1', true)
os.sleep(65)
grp.write('32/1/1', false)
os.sleep(70)
Threads: 42
Code: --Set temperature
Tc = '11/0/5' -- 09.001 Temperature (2Bytes)
--Reference Temperature
TRef = '11/0/20' -- 09.001 Temperature (2Bytes)
--Output object that enables resident script
addr = '11/0/32' --01. 1 bit (boolean)
--Countdown in days
RstDays = '11/0/31' --1 Bytes unsigned integer
--Countdown in hours
RstHours = '11/0/30' --1 Bytes unsigned integer
if delta >= (((grp.getvalue(RstDays)*60)*24) + (grp.getvalue(RstHours)*60)) * 60 then
grp.write(Tc, grp.getvalue(TRef))
Hello, I modified this script to reset the temperature of a pool. How can I embed a 250 Byte String object for the remaining time state?
This will send a string like 1d 4h 3m to 1/1/1:
Code: delta = os.time() - obj.updatetime
timeout = ((RstDays) * 24 + (RstHours)) * 60 * 60
remaining = math.max(0, delta - timeout)
days = math.floor(remaining / 86400)
hours = math.floor((remaining % 86400) / 3600)
minutes = math.floor((remaining % 3600) / 60)
txtremaining = days .. 'd ' .. hours .. 'h ' .. minutes .. 'm'
grp.update('1/1/1', txtremaining)
if remaining == 0 then
Threads: 42
(25.01.2021, 09:08)admin Wrote: This will send a string like 1d 4h 3m to 1/1/1:
Hello Admin, something is not right since the account is ascending.
Try changing "delta - timeout" calculation in line 3 to "timeout - delta"
Threads: 42
26.01.2021, 10:54
(This post was last modified: 27.01.2021, 07:36 by davidchispas.)
(25.01.2021, 17:04)admin Wrote: Try changing "delta - timeout" calculation in line 3 to "timeout - delta"
--Countdown in days
timeout = (grp.getvalue(RstDays) * 24 + grp.getvalue(RstHours)) * 60 * 60
remaining = math.max(0, timeout - delta)
txtremaining = days .. 'd ' .. hours .. 'h ' .. minutes .. 'm '
grp.checkupdate('11/0/33', txtremaining)
Ok thanks, that's how it works. I want to get the counter reset to 0 when 'Tc' == 'TRef'. What can I add to the script?
This script runs every 1 second to be immediate, but the timer status sends it every second, I changed it to check.uptade to correct that. My question is if it is better like this or run it every 60 seconds ....?
To take advantage of this script to other functions, can I add seconds? I have tried but without positive result.
Threads: 42
27.01.2021, 08:47
(This post was last modified: 27.01.2021, 08:50 by davidchispas.)
Hello, a very strange thing happens to me and I cannot find an explanation.
With this script I send the time status of the countdown (I had to change the data type to '14 bytes ASCII string 'to be able to view it on a KNX screen.
The rest of the objects work perfectly and are displayed on the KNX bus, but the 14-byte object, when updated (it is perfectly green) in LM, is not sent to the bus and is not reflected on my screen. But if I send the value manually from the LM configuration panel, it is sent, also if I make a status request.
Where can the error be?
Change checkupdate to checkwrite, update does not send to the TP bus.
For seconds use this:
Code: seconds = remaining % 60
txtremaining = days .. 'd ' .. hours .. 'h ' .. minutes .. 'm ' .. seconds .. 's'
Threads: 42
(27.01.2021, 08:50)admin Wrote: Change checkupdate to checkwrite, update does not send to the TP bus.
Ah okay, I did not know this information. Thank you very much for your help!