Threads: 42
I need to create a script that when '1/1/1' is "on" it starts a cyclic generator of time of 'on' and 'off' parameterizable.
When '1/1/1' is Off, the cyclic generator is reset and the output is Off.
Threads: 31
Use event script on 1/1/1 to enable/disable a resident script which will send what you need.
Threads: 42
(24.08.2020, 07:10)Daniel. Wrote: Hi
BR Thanks Daniel, you can provide me with an example that I did not find in the search engine, or help me with the script.
1/1/1 - Activate sequence
1/1/2 - Time value activated
1/1/3 - Time value disabled
1/1/4 - Output object
Threads: 31
What does the tow objects:
Supposed to be doing?
Threads: 42
(24.08.2020, 10:50)Daniel. Wrote: What does the tow objects:
Supposed to be doing? In these integer value objects, I enter a time in minutes.
I need to create a cyclic send of different on / off values. For example, 10 minutes on / 30 minutes off. This sequence is continuous while 1/1/1 is enabled, when changing everything is off.
Threads: 31
Event script attached to 1/1/1
Code: value = event.getvalue()
if value then
script.enable('cycle_scriptname')
script.disable('cycle_scriptname')
cycle_scriptname replace with a name of resident script.
Resident script of interval 60s
Code: timerOn = grp.getvalue('1/1/2')
timerOff = grp.getvalue('1/1/3')
onCounter = storage.get('onCounter', 0)
offCounter = storage.get('offCounter', 0)
onCounter = onCounter +1
offCounter = offCounter +1
log(onCounter,offCounter)
if onCounter >= timerOn then
grp.write('1/1/4', true)
storage.set('onCounter', 0)
storage.set('onCounter', onCounter)
if offCounter >= timerOff then
grp.write('1/1/4', false)
storage.set('offCounter', 0)
storage.set('offCounter', offCounter)
Threads: 42
24.08.2020, 16:25
(This post was last modified: 24.08.2020, 16:26 by davidchispas.)
if value then
Thanks Daniel, I'm testing it but I can't get it to work properly. I have set 1 minute on and 2 minute off.
I have temporarily changed 1/1/4 to 0/5/3.
Threads: 31
I left you the log which shows the counting for on and off. For testing change the script interval to 10. It will then run tomerOn x 10s instead of 60s. Make sure you change 1/1/4 in both places.
Add to event script under else condition
so the counter is rested after disabling it.
Threads: 42
25.08.2020, 09:07
(This post was last modified: 25.08.2020, 13:32 by davidchispas.)
(24.08.2020, 16:40)Daniel. Wrote: I left you the log which shows the counting for on and off. For testing change the script interval to 10. It will then run tomerOn x 10s instead of 60s. Make sure you change 1/1/4 in both places.
Hi Daniel, I had to modify in the resident script to send the opposite value for it to work correctly.
if onCounter> = timerOn then
grp.write ('1/1/4', false)
storage.set ('onCounter', 0)
Anyway, I would like to thank you for your indications that have been of great help to me!
In the end it has remained like that, I share it in case someone is of help.
Code: AddressOutput = '1/1/4' -- 01. 1 bit (boolean)
StatusCounterOn = '1/1/5' --05. 1 byte unsigned integer
StatusCounterOff = '1/1/6' --05. 1 byte unsigned integer
CounterOn = 'onCounter_Test'
CounterOff = 'offCounter_Test'
Script = 'Test'
if value then
script.enable(Script)
script.disable(Script)
sleep(2)
grp.checkwrite(AddressOutput, false)
storage.set(CounterOn, 0)
storage.set(CounterOff, 0)
grp.checkwrite(StatusCounterOn, 0)
grp.checkwrite(StatusCounterOff, 0)
--Opcional
sleep(2)
storage.delete(CounterOn)
storage.delete(CounterOff)
Code: --Script resident (60s)
AddressInput= '1/1/1' -- 01. 1 bit (boolean)
timerOn = '1/1/2' --05. 1 byte unsigned integer
timerOff = '1/1/3' --05. 1 byte unsigned integer
AddressOutput= '1/1/4' -- 01. 1 bit (boolean)
onCounter = storage.get('onCounter_' .. _SCRIPTNAME, 0)
offCounter = storage.get('offCounter_' .. _SCRIPTNAME, 0)
if grp.getvalue(AddressInput) and grp.getvalue(AddressOutput) then
if grp.getvalue(AddressInput) and not grp.getvalue(AddressOutput) then
if onCounter >= grp.getvalue(timerOn) then
grp.write(AddressOutput, false)
storage.set('onCounter_' .. _SCRIPTNAME, 0)
storage.set('onCounter_' .. _SCRIPTNAME, onCounter)
if offCounter >= grp.getvalue(timerOff) then
grp.write(AddressOutput, true)
storage.set('offCounter_' .. _SCRIPTNAME, 0)
storage.set('offCounter_' .. _SCRIPTNAME, offCounter)
grp.checkwrite(StatusCounterOn, onCounter)
grp.checkwrite(StatusCounterOff, offCounter)
