Threads: 17
Hi:
How can I Know that the bus KNX is disconnected outside Alerts. I want to send an email to know that situation.
Threads: 60
So is there a way to do this? Is there a way to get specific alerts to generate an email?
Thanks,
Roger
Threads: 40
Yes, via a resident script:
Code: if not client then
function statushandler(status)
if status == 0x00 then
-- KNX Connected
elseif status == 0xFF then
-- KNX Disconnected
client = require('localbus').new(1)
client:sethandler('status', statushandler)
client:step()
Threads: 40
Good. Is there a way to fo the same with knx physical adresses as well? I was thinking to maybe ones a day run a script that checks programmed adresses and makes an alert if trouble and and ok message to the log if ok
Threads: 40
There's knxlib.ping(phys_addr) function that you can use. But it will work only if your LM has direct KNX/TP connection.
Threads: 40
Ok. Thx. Yes i have tp so that will work
Threads: 60
(21.02.2017, 08:35)admin Wrote: Yes, via a resident script:
-- KNX Connected
-- KNX Disconnected
client:step()
Thank you. I added the function into the group address status script. From before.
Threads: 13
30.08.2021, 20:27
(This post was last modified: 31.08.2021, 05:46 by morkovka.)
(22.02.2017, 01:47)rocfusion Wrote: (21.02.2017, 08:35)admin Wrote: Yes, via a resident script:
-- KNX Connected
-- KNX Disconnected
client:step()
Thank you. I added the function into the group address status script. From before. I tried this function and it's not working in the current version of Wiser - does anyone have a current working version of this function to check the local KNX TP link?
Tried in a resident script and scheduled script (I prefer scheduled script), anyway the statushandler() function never gets called.
Thank you!
Morkov
Threads: 1
I tested it with Wiser for KNX with firmware 2.6.2 and it was working for me.
You have to use resident script with sleep time 0.
(30.08.2021, 20:27)morkovka Wrote: (22.02.2017, 01:47)rocfusion Wrote: (21.02.2017, 08:35)admin Wrote: Yes, via a resident script:
-- KNX Connected
-- KNX Disconnected
client:step()
Best regards
forsterm
Threads: 13
Strange, I wonder what am I doing wrong.
I'm using this, in a resident script with sleep time 0:
Code: -- KNX TP connectivity check
log('KNX connection check succesful')
alert('KNX is disconnected')
log('status is ' .. tostring(status))
client:step()
And I get nothing in the logs, error logs, alerts... any ideas?
(31.08.2021, 06:36)forsterm Wrote: Hi,
-- KNX Connected
-- KNX Disconnected
client:step()
Thank you!
Morkov
Threads: 40
You won't get any log until the connection status changes. If you want to get the current status the use status = buslib.isconnected()
Threads: 13
(31.08.2021, 07:53)admin Wrote: You won't get any log until the connection status changes. If you want to get the current status the use status = buslib.isconnected()
Thank you, that works well!
What's the difference between 'knxlib' and 'buslib'?
Thank you!
Morkov
Threads: 40
No difference, both variables reference the same library functions
Threads: 15
What can be the reason for KNX / TP disconnected messages?
In my alerts, I have many messages from KNX / TP connected and KNX / TP disconnected, but I do not know why.
Threads: 40
Which hardware version do you have?
Threads: 15
HW: LM5 Lite (i.MX6)
SW: 20200703
Threads: 13
I also experience this, once every few days - in the Error log I see:
Quote:KNX/TP: Transmitter Error (send 0 receive 1)
And in the Alerts log, at the same exact time (same second), it says:
Quote:KNX/TP: Connected
Using W4K i.MX6.
Thank you!
Morkov
Threads: 40
Transmitter error and temperature warning usually means that there are too many devices on the KNX line.
Threads: 13
(01.10.2021, 14:06)admin Wrote: Transmitter error and temperature warning usually means that there are too many devices on the KNX line.
What temperature warning? I don't see it.
Just the transmitter error coupled with a 'connected' (as if the device's KNX line was disconnected and reconnected)
Thank you!
Morkov
Threads: 40
Temperature warning is another indication of an overloaded line. It's not guaranteed to appear though. The more devices are on the KNX line the harder it is to transmit data. This leads to the chip overheating and/or not being able to transmit at all (send 0 receive 1 error).