Modbus telegrams bus traffic
Hello guys!
I need your help.
In a project i have modbus integration through W4K.
There is a problem as you can see in the pictures.
I have a lot of bus traffic with some temperature telegrams.
Is there any way to limit this traffic?
Is there any script or any adjustment to work around this issue?
Set it to send on change of value.
Value send delta: - change from 0 to a value
Thank you Daniel!
I can not find this setting.
Can you help me?
Thank you Daniel for you reply!
Seems that I dont have this feature in wiser 4 knx homelynk.
Upload your profile here
.json   Daikin_rtd_w.json (Size: 19.04 KB / Downloads: 5)
Change "bus_datatype": "temperature", to "bus_datatype": "float16",
This should work but seems there is little bug.
Thank you Daniel!
What is value send Delta?
So it means that if i change it from 0 to 1, it will sends values only if it changes by one degree Celsius?
yes
can you tell me what exactly this mean?
it just update the value to the groepadres if there is a change of 1,0 or when there is a changing of 0,1 or less?
If you put 1 then value will be sent if the change will be at last 1 or higher.
Thanks for reply , Daniel