Threads: 20
I had the idea grp.checkwrite / grp.checkupdate don't work always.
Are there limitation about when I can use it and when not?
Maybe not all datatype?
It looks like it doesn't always update the new value or do I look wrong?
I understand grp.checkwrite is when it has to write to the KNX bus
and grp.checkupdate if it is just local for the LM.
Threads: 31
grp.checkwrite is sending to TP and IP but on change of value. grp.checkupdate is sending only to IP but also on change of value.
Threads: 20
Oké thanks.
I think my problem was also not the right data type.
Threads: 21
and grp.write always send the value on TP and IP, even if the value inside LM is up to date?
For floating point values default delta is 0.1. The difference between values is lower in your case.
Threads: 20
Oké thanks, does it means I need to take another data type for solving this problem?
The value will update when the difference is large enough. You can also specify delta manually as the third argument. Try 0.01 or 0.001
Threads: 20
Sounds interesting, do you have an example of this?
Threads: 20
Great tanks, that was what I was looking for ?
Threads: 7
27.11.2024, 08:46
(This post was last modified: 27.11.2024, 10:10 by Ranjeet.)
Hii sir ,
I have created resident script in which when a light ON in particular area it sends command to another object which tells me that a light is ON in this area the problem is that when i Active this script then logic machine become a slow or hang.and script sleep interval time is 0 second.
Can you suggest me solution for this query.
here is script --
-- Define the function that will run every 5 seconds
function checkValues()
-- Get the values from the grp (assuming grp.getvalue() returns the values for these keys)
value = grp.getvalue('0/6/2')
value2 = grp.getvalue('0/6/10')
value3 = grp.getvalue('0/5/6')
value4 = grp.getvalue('0/6/8')
value5 = grp.getvalue('2/5/22') -- value5 is checked for >= 1
value18 = grp.getvalue('2/5/27') -- value18 is checked for >= 1
value19 = grp.getvalue('0/6/44') -- value19 is checked for >= 1
value20 = grp.getvalue('0/6/25') -- value20 is checked for >= 1
value21 = grp.getvalue('0/6/58') -- value21 is checked for >= 1
value22 = grp.getvalue('0/6/30') -- value22 is checked for >= 1
-- Adjust the conditions for clarity (use parentheses to ensure proper evaluation order)
if (value or value2 or value3 or value4 or value5 >= 1 or
value18 >= 1 or value19 >= 1 or value20 >= 1 or
value21 >= 1 or value22 >= 1) then
grp.write('0/6/65', true) -- Write true if any condition is met
grp.write('0/6/65', false) -- Write false otherwise
-- Set the script to run every 5 seconds
while true do
checkValues() -- Call the function to check values
os.execute("sleep 5") -- Sleep for 5 seconds before checking again
Threads: 31