This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Short - Long press
#1
Here's a simple script that calculate the time difference between 1 (true) and 0 (false) of a 1 bit object.
I have extended it with some examples on how to use it to calculate the ON time of an object and as a working hour timer.
 
Code:
long = 10 --set long press in seconds

value = event.getvalue()
object = grp.find(event.dst)

if value then
  if not storage.get('start') then
    storage.set('start', object.updatetime)
  end
else
  start = storage.get('start')
  if start then
      diff = os.difftime(object.updatetime, start)
  end
  storage.delete('start')
end

if diff then
  if diff >= long then
    --long press time in seconds
      log('long press: '..diff..' seconds') 
    else
    --short press time in seconds
      log('short press: '..diff..' seconds')
  end
  --time the object was ON in seconds
  log('object was ON for: '..diff..' seconds')
 
    hour = math.floor((diff / 3600)+ 0.5)

    if not storage.get('counter') then
    counter = hour
      storage.set('counter', counter)
    else
      counter = storage.get('counter')
      counter = counter + hour
      storage.set('counter', counter)
    end
      --total time the object was ON in hours
      log('hour counter: '..counter..' hours')
end