This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Air conditioning
#2
Hello, here is a script, you can make it resident.

Code:
summer = grp.getvalue('6/1/1') -- boolean if '0' is winter, if '1' is summer winter = not summer   current = grp.getvalue('5/1/14') setpoint = grp.getvalue('5/2/14') running = grp.getvalue('6/1/0') ~= 0 hysteresis = 0.5 value = nil if (running and summer) then   if current < (setpoint - hysteresis) then     value = 0 -- off   end elseif (summer and current > (setpoint + hysteresis) ) then   value = 9 -- cooling end if(running and winter) then   if current > (setpoint + hysteresis) then     value = 0 -- off   end elseif (winter and current < (setpoint - hysteresis) ) then   value = 3 -- heating end if value then   grp.write('6/1/0', value) end
Reply


Messages In This Thread
Air conditioning - by Danny - 17.06.2022, 08:58
RE: Air conditioning - by RomansP - 17.06.2022, 13:17