1 script 200 Rooms
Hi, I have this script, but 200 rooms. What will the script look like when it is based on finding room number. 1 script for all my rooms?
Instead of 200 scripts. The room number is 1.203 in this case.
XXXXX_XZXX - XXX.XXX-SQXXX-room_Setpoint_XXX this line can be different..
433011_XZ30 - 360.004-SQ401-1.203_Setpoint_mp4
Comp_max_input1 = grp.getvalue('1.203-SX601_Cooling_C')
Comp_max_input2 = grp.getvalue('1.203-RB601_SQ_C')
Comp_max_output = '433011_XZ30 - 360.004-SQ401-1.203_Setpoint_mp4'
maxout = math.max(Comp_max_input1,Comp_max_input2)
grp.checkwrite(Comp_max_output, maxout)
Do you follow a specific addressing scheme where other addresses can be calculated from the source address?
Something like 1/1/203 - input1, 1/2/203 - input2, 3/2/203 - output.
(12.04.2022, 08:55)admin Wrote: Do you follow a specific addressing scheme where other addresses can be calculated from the source address?
No.
Is there some rule how other names can be found from the source name? Another option is to tag objects with multiple tags (something like "input", "room_1_203") and find other objects using these tag. Or you can create a lookup table with all addresses that the script will use to find input/output objects.
(12.04.2022, 09:17)admin Wrote: Is there some rule how other names can be found from the source name? Another option is to tag objects with multiple tags (something like "input", "room_1_203") and find other objects using these tag. Or you can create a lookup table with all addresses that the script will use to find input/output objects.
No this is what I have. What is the simplies way to do this with what i got?
Here's a solution with a lookup table. All input objects should have a common tag to which an event script is attached. Fill the addrlist table with group addresses as needed. Each entry is a single room (input 1/2 + output).
The script finds the second input based on the group address that triggered the script and writes the maximum between two inputs to the output object.
123456789101112131415161718192021222324252627282930313233343536
addrlist = {   {     input1 = '1/1/1',     input2 = '1/1/2',     output = '1/1/3',   },   {     input1 = '1/1/4',     input2 = '1/1/5',     output = '1/1/6',   },   {     input1 = '1/2/4',     input2 = '1/2/5',     output = '1/2/6',   }, } for _, addrs in ipairs(addrlist) do   if event.dst == addrs.input1 then     altinput = addrs.input2     output = addrs.output     break   elseif event.dst == addrs.input2 then     altinput = addrs.input1     output = addrs.output     break   end end if altinput and output then   value1 = event.getvalue()   value2 = grp.getvalue(altinput)   grp.checkwrite(output, math.max(value1, value2)) end
(13.04.2022, 11:21)admin Wrote: Here's a solution with a lookup table. All input objects should have a common tag to which an event script is attached. Fill the addrlist table with group addresses as needed. Each entry is a single room (input 1/2 + output).
TNX