15.04.2025, 12:48
Is the GND connected between devices?
------------------------------
Ctrl+F5
Ctrl+F5
Modbus profiles examples
|
28.04.2025, 05:48
(15.04.2025, 12:48)Daniel Wrote: Is the GND connected between devices? Hi, The Modbus master device does not have a GND connection (see attachment ECP202EXP.PNG).
28.04.2025, 07:20
Check all suggestions from this thread
https://forum.logicmachine.net/showthrea...2#pid38562
------------------------------
Ctrl+F5
28.04.2025, 12:12
It's possible that INP-GND or PROBE-G can be used. Power down the unit and check resistance between INP-GND and PROBE-G. Most likely inputs are not isolated and resistance should be close to 0. Then check the resistance between RS485-A and INP-GND / RS485-B and INP-GND. Report the values that you get.
|
« Next Oldest | Next Newest »
|