Modbus profiles examples
Is the GND connected between devices?
(15.04.2025, 12:48)Daniel Wrote: Is the GND connected between devices?
The Modbus master device does not have a GND connection (see attachment ECP202EXP.PNG).
Check all suggestions from this thread
https://forum.logicmachine.net/showthrea...2#pid38562
It's possible that INP-GND or PROBE-G can be used. Power down the unit and check resistance between INP-GND and PROBE-G. Most likely inputs are not isolated and resistance should be close to 0. Then check the resistance between RS485-A and INP-GND / RS485-B and INP-GND. Report the values that you get.
(21.11.2024, 13:37)admin Wrote: If you need a profile for ABB B23 112-10M then we can help with creating it.
Hii sir Sorry for this threat. I need profile for ABB B23 112-10 please help me to create this
See the attached profile. It's not tested so some modifications might be needed. Use Modbus profiler app for this: https://forum.logicmachine.net/showthread.php?tid=5911
.json   abb_b21_b23_b24.json (Size: 6.56 KB / Downloads: 14)