Mod_bus problem
Hi, I'm trying to add a device with modbus but result is not as expected.
Problem 1:
value_custom is not added to objects.
{  "manufacturer": "xxx",  "description": "xxx",  "mapping":[      { "name": "320000 - SV - Varme System Anleggs modus", "bus_datatype": "int16", "type": "register", "address": 1651, "datatype": "int16",      "bus_address": "32/0/40", "value_custom": { "0": "Stoppet", "1": "Startet" } }  ] }
Problem 2:
When trying to get value_bitmask i get 1 on all objects. The hexvalue is 0003 and should give value 1 in first 2 objects.
1234567891011121314
{  "manufacturer": "xxx",  "description": "xxx",  "mapping":[    { "name": "370000.JP401 Start", "bus_datatype": "bool", "type": "register", "address": 1530, "datatype":"int16", "bus_address": "32/0/0",       "value_bitmask": "0x00"},    { "name": "370000.JP401 Drift", "bus_datatype": "bool", "type": "register", "address": 1530, "datatype":"int16", "bus_address": "32/0/1",       "value_bitmask": "0x01"},    { "name": "370000.JP401 Feil", "bus_datatype": "bool", "type": "register", "address": 1530, "datatype":"int16", "bus_address": "32/0/2",       "value_bitmask": "0x02"},    { "name": "370000.JP401 Kritisk alarm", "bus_datatype": "bool", "type": "register", "address": 1530, "datatype":"int16", "bus_address": "32/0/3",       "value_bitmask": "0x03"}   ] }
1. Custom values are not used when bus_address is specified directly, it will only be used when creating object mapping manually from UI
2. Bitmask cannot be zero, correct bitmask should be 1, 2, 4 and 8 for each bit starting from lowest one:
0001b = 1
0010b = 2
0100b = 4
1000b = 8
(23.01.2018, 10:48)admin Wrote: 1. Custom values are not used when bus_address is specified directly, it will only be used when creating object mapping manually from UI
0001b = 1
0010b = 2
0100b = 4
1000b = 8
Thanks!
Problem 3:
I have an int32 value that is split up into two int16 and i can't get the value i need. I have tried read_offset 0 and 1 and value_nan but i don't realy get it.... Is there an other method?
1234567891011121314
{   "manufacturer": "xxx",   "description": "xxx",   "mapping":[         { "address": 1005, "name": "320000.IE001.PV1", "read_offset": 1, "bus_datatype": "float16", "datatype": "float32",       "value_multiplier": 0.1, "units": " kW"},     { "address": 1006, "name": "320000.IE001.PV2", "read_offset": 1, "bus_datatype": "float16", "datatype": "float32",       "value_multiplier": 0.1, "units": " °C"},     { "address": 1007, "name": "320000.IE001.PV3", "read_offset": 1, "bus_datatype": "float16", "datatype": "float32",       "value_multiplier": 0.1, "units": " °C"}   ] }
Do not use read_offset and set datatype to int32. You might need to set read_swap depending on byte/word order of your Modbus device. The easiest way to check it is to use RTU read test in Modbus tab. Also consider using float32 for bus_datatype since float16 has limited precision range and does not work well for large values.