Hi everyone! I have dim DALI problem on LM. Do you have a solution to help me? It is turned off quickly or turned on quickly, annoying customers
I want dim from 0% to 100% or from 100% to 0% to have a period. For example it will take 5s to complete the event,. In the settings section there is no time.
Thank so much!
You can change fade time of ballasts via a script. Fade time setting 6 is approximately 4 seconds, the larger the value the longer the fade time.
Run this once (assuming you are using internal gateway):
require('user.dali')
dalicmd('internal', 'setdtr', { addrtype = 'broadcast', value = 6 })
dalicmd('internal', 'storefadetime', { addrtype = 'broadcast' })
I also suggest looking into our CANx-DALI gateway which provides a lot more features than the internal or old RS-485 gateways.
Thank so much , everyone ! Admin !
I have seen it work well! But I do not understand where it will store this information? Smile. But there is something I do not understand, when I do this, my on / off address 11/1/1 it also works dim, I do not want that, I only need 11/1/3 dimmer address. Can it change you? Smile
And I also want to Get the entire state of the light, and bring it up to update. I have tried but it's failed? Help me please. Sad
res, err = dalicmd('internal', 'querystatus', { addrtype = 'broadcast' })
if res then
log(res:byte())
log(err)
You can try using a script instead of object mapping for binary light control. This event script must be mapped to a binary object. It will control ballast with short address 1.
cmd = event.getvalue() and 'recallmax' or 'off'
res, err = dalicmd('internal', cmd, { addrtype = 'short', address = 1 })
As for status you cannot use broadcast if you have more than 1 ballast. All ballasts will reply to broadcast query which will result in a collision error. Use short address mode for queries:
res, err = dalicmd('internal', 'querystatus', { addrtype = 'short', address = 0 })
thank Admin !
I do not quite understand! For example, my dimmer is 11/1/3, I want to receive status at 11/1/103. How do I add the code? I really thank you, I'm new. Sad
Use a resident script with 5-10 seconds of sleep time.
if res then
  grp.checkupdate('11/1/103', res:byte())
res, err = dalicmd('internal', 'querystatus', { addrtype = 'short', address = 1 })
if res then
  grp.checkupdate('11/1/104', res:byte())
I love you every one ! Smile
Thank so much !
I try! but...Sad
Everyone let me ask! Why is my value not returning as current value? 11/1/3 other than 11/1/103 (status). 11/1/4 other than 11/1/104 (status). 30% and 51%, but it's 4% and 4%. Please help me!
if res then
if res then
You need to use queryactual instead of querystatus command.
Try this script:
function queryactual(short, addr)
  local res, err = dalicmd('internal', 'queryactual', { addrtype = 'short', address = short })
  if res then
    local val = res:byte()
    if val > 0 then
      val = math.floor(val / 2.54 + 0.5)
      val = math.max(1, val)
    grp.checkupdate(addr, val)
queryactual(0, '11/1/103')
queryactual(1, '11/1/104')