This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Delay for DALI !
#20
(03.06.2020, 06:11)admin Wrote: You need to use queryactual instead of querystatus command.
Try this script:
Code:
require('user.dali')

function queryactual(short, addr)
  local res, err = dalicmd('internal', 'queryactual', { addrtype = 'short', address = short })
  if res then
    local val = res:byte()
    if val > 0 then
      val = math.floor(val / 2.54 + 0.5)
      val = math.max(1, val)
    end
    grp.checkupdate(addr, val)
  end
end

queryactual(0, '11/1/103')
queryactual(1, '11/1/104')

I need your opinion on how it is advisable to obtain the status of the ballasts in group.

For example, a group of 60 ballasts linked to the same control object. To visualize the real state I need to obtain at least the state of one of them, but in the event that in the future that ballast fails, could I assign the same address to the 60 ballasts?

To visualize the On / Off status, I added another line to the script, is that fine, or is it recommended to do it in another way?

Code:
require('user.dali')

function queryactual(short, addr)
  local res, err = dalicmd('internal', 'queryactual', { addrtype = 'short', address = short })
  if res then
    local val = res:byte()
    if val > 0 then
      val = math.floor(val / 2.54 + 0.5)
      val = math.max(1, val)
    end
    grp.checkupdate(addr, val)
  end
end

queryactual(0, '1/1/0') --Porcentage
queryactual(0, '1/2/0') --1Bit
queryactual(1, '1/1/0') --Porcentage
queryactual(1, '1/2/0') --1Bit
queryactual(2, '1/1/0') --Porcentage
queryactual(2, '1/2/0') --1Bit
Reply


Messages In This Thread
Delay for DALI ! - by phongvucba - 01.06.2020, 06:31
RE: Delay for DALI ! - by admin - 01.06.2020, 06:52
RE: Delay for DALI ! - by phongvucba - 02.06.2020, 03:55
RE: Delay for DALI ! - by admin - 02.06.2020, 07:44
RE: Delay for DALI ! - by phongvucba - 02.06.2020, 08:06
RE: Delay for DALI ! - by admin - 02.06.2020, 11:28
RE: Delay for DALI ! - by phongvucba - 02.06.2020, 16:08
RE: Delay for DALI ! - by phongvucba - 03.06.2020, 03:32
RE: Delay for DALI ! - by admin - 03.06.2020, 06:11
RE: Delay for DALI ! - by davidchispas - 04.01.2021, 09:59
RE: Delay for DALI ! - by phongvucba - 14.11.2020, 07:17
RE: Delay for DALI ! - by admin - 14.11.2020, 08:05
RE: Delay for DALI ! - by phongvucba - 14.11.2020, 09:15
RE: Delay for DALI ! - by Daniel - 16.11.2020, 08:40
RE: Delay for DALI ! - by phongvucba - 01.12.2020, 11:27
RE: Delay for DALI ! - by davidchispas - 24.11.2020, 10:46
RE: Delay for DALI ! - by admin - 24.11.2020, 10:48
RE: Delay for DALI ! - by admin - 24.11.2020, 10:58
RE: Delay for DALI ! - by davidchispas - 24.11.2020, 11:12
RE: Delay for DALI ! - by Daniel - 01.12.2020, 11:30
RE: Delay for DALI ! - by admin - 04.01.2021, 10:58
RE: Delay for DALI ! - by davidchispas - 05.01.2021, 09:34
RE: Delay for DALI ! - by admin - 05.01.2021, 09:36
RE: Delay for DALI ! - by davidchispas - 13.01.2021, 10:47
RE: Delay for DALI ! - by Daniel - 13.01.2021, 11:00

Forum Jump: